I am looking for a chart that will give me the line sizing from different pressure drop and temperature from the lbs/min of the HFC refrigerant (R-134a, R-404a, R410a). Such as the old ASRHAE RP 185 book and refrigerant line sizing (R-22, R-12, R-502, R717).

Best wishes for 2003

kathleen

Prof Sporlan
30-12-2002, 05:07 PM
Kathleen, ASHRAE's 2002 Refrigeration Handbook has published line capacities for for R-134a, R-404A, and R-410A (see chapter 2). You may also find Sporlan's Form 5-162 interesting. It lists line capacites for R-134a and R-404A, but not R-410A at the moment. It also contains useful refrigerant data, conversion factors, thermodynamic terms, etc. You local Sporlan rep or wholesaler can get this for you.

Kathleen
30-12-2002, 06:28 PM
Hello Prof sporlan,

In chapter 2 of ASRHAE they give a fast chart but not by lbs/min with different choice of pressure drop, therefore we can decide if it is better to increase or reduce the line sizing.

I do not have the sporlan one but I will ask for it. Because I would like to review my line sizing for the problem I have with capacity problem. And the chart I use was a fast one in tonnage only, with different line length and I think they might be to short. And a real flow density chart will be of good help.

best regards

Kathleen

Andy
30-12-2002, 07:51 PM
Hi, Kathleen:)
I don't use charts, I'am just to lazy to look them up. What I do use is a pipe sizing program from Danfoss called DirCal, this can be downloaded for free from there web site.
Danfoss Selection Software (http://uk.refrignet.danfoss.com/SW/UKRA_Product_Selection_openNet/en_gb/index.htm?click=c_{F57E407C-3A95-4B78-9239-F860369F0FFB})
Alternativly they may send it to you by post if you ask nicely.
If you have any problems on using it it drop me an email, it's very good when you get it figured out.
Regards. Andy.

Jahangir
14-02-2007, 04:22 PM
can i have a copy of this software?

Kathleen
14-02-2007, 07:22 PM
I receive my software which works really easy by my danfoss rep.

Brian_UK
14-02-2007, 07:54 PM
Hi Kathleen,

Glad to see that you resolved your query here and it's good to see you back with us. ;)

Kathleen
14-02-2007, 08:01 PM
Hi Brian

be sure refrigeration is my passion, I am always a email closed

Josip
14-02-2007, 11:02 PM
Hi, Jahangir :)


can i have a copy of this software?

Of, course;)

follow this link:
http://www.danfoss.com/United_Kingdom/BusinessAreas/Refrigeration+and+Air+Conditioning/Products/Product+Selection+Tools.htm

register and download what you need.
CoolCat, ForeseeT, CoolSelector, RS+3, DIRCalc or DanCap™ 1.0

or this one:

http://www.danfoss.com/United_Kingdom/NewsAndEvents/News/RA+Solutions/Fitters+Notes.htm

Very good fitters notes

Best regards, Josip:)

fmchadyai
15-02-2007, 09:25 AM
Page5 to Page7

fmchadyai
15-02-2007, 09:27 AM
Page8 to Page9

fmchadyai
15-02-2007, 09:35 AM
Page11 to Page15

Josip
17-02-2007, 04:17 PM
Hi, all :)


Hi, Jahangir :)

Of, course;)

follow this link:
http://www.danfoss.com/United_Kingdom/BusinessAreas/Refrigeration+and+Air+Conditioning/Products/Product+Selection+Tools.htm

register and download what you need.
CoolCat, ForeseeT, CoolSelector, RS+3, DIRCalc or DanCap™ 1.0

or this one:

http://www.danfoss.com/United_Kingdom/NewsAndEvents/News/RA+Solutions/Fitters+Notes.htm

Very good fitters notes

Best regards, Josip:)

Sorry, above link is to an old Version of DirCalc113;)

Here is new Version DirCalc114

http://www.danfoss.com/NR/rdonlyres/F82F90C3-D61E-4F07-A42C-D23C7C2353DE/0/DirCalc114.zip

also for other software:

http://www.danfoss.com/Pacific/BusinessAreas/Refrigeration+and+Air+Conditioning/Products/Product+Selection+Tools.htm

Best regards, Josip :)

alfredobertiz
25-10-2007, 07:06 AM
hello there
How can i eliminate condensation in the ducting system. The ducting was locted near the kitchen it was insulated with 1" thick rubber insulation

sanchezbond007
08-11-2007, 01:55 AM
I want to make a custom evaporator or barrel that works like a chiller I have a condensing unit of 30,000 BTU. with refrigerant 22, i need ideas for the calculation or how to do it.

Robertoroli
06-12-2007, 04:44 PM
Hi to all,

Anyone have the tables for sizing ammonia piping? I dont have the ASHRAE or IIAR handbook. So if somebody can pass me this information i will be very thankful

Josip
06-12-2007, 10:54 PM
Hi, Robertoroli :)


Hi to all,

Anyone have the tables for sizing ammonia piping? I dont have the ASHRAE or IIAR handbook. So if somebody can pass me this information i will be very thankful

Please check the links in above post #13...there you have everything...

Best regards, Josip :)

SURESH YADAV
15-12-2008, 11:26 AM
thanks buddy it is realy useful to me

lode janssens
29-05-2009, 03:07 PM
Katleen,

Go to R717.com and apply for the Free Ammonia Refrigeration Piping Calculator.