PDA

View Full Version : R12 to R22



NickScotland
14-07-2007, 06:49 PM
I've been working on a Williams chiller in the North Sea, the work scope was to come out and repair a section of pipe work, ended up being the hot gas line for the drip tray. Was told that the refrigerant was R22. However i noticed a small label mostly peeled away that said R12, the system had been working for a while.

Is R12 banned yet? I think they may have done a full conversion however my discharge pressure is really high (290psi), it is in the kitchen so this may be the reason, but could it be that the condenser coil is sized for R12 and not R22, would this make a difference?

The unit is working but i just ain't confident in it.

Cheers

Nick

Brian_UK
14-07-2007, 06:55 PM
If you don't know the status of R12 in the Eu/UK what are you doing working with refrigerants?

You need to get it analysed if you are not sure.