shaun spencer
22-09-2002, 01:42 AM
What is up with Hussmann QA lately
had constuction guys install 18 doors last week, went to start up 13 doors (5-5-3) had fans come on at ambient, fan relays 220 on a 110 cntrl cct
had 44 ft produce installed, on start up two tev with dead power heads.
a real piss off

any comments dan??

Dan
22-09-2002, 04:32 AM
What is up with Hussmann QA lately
had constuction guys install 18 doors last week, went to start up 13 doors (5-5-3) had fans come on at ambient, fan relays 220 on a 110 cntrl cct
had 44 ft produce installed, on start up two tev with dead power heads.
a real piss off


Is it possible that somebody didn't order the equipment correctly?

As far as powerheads go, I would need more information. Hussmann doesn't manufacture powerheads.

If you see your problem as a Hussmann problem, let's get it on. I will resolve it with you.

shaun spencer
22-09-2002, 11:49 AM
dan - was ordered right,
was 4 sets of doors, 3 of them had 220 fan relays 1 had a 110 fan relay all 4 had 110 antisweat relays, found this problem at 530 am after working from 600 am the day before. was not impressed

Dan
22-09-2002, 01:12 PM
I just forwarded your letter to the head of quality control. His name is Chuck Macchia, if you need to speak to him. 1 314 291 2000. Chuck_Macchia@irco.com.

Hussmann will reimburse you for your labor, just make sure you have models and serial numbers on your work orders.

If you need follow-up, let me know. Sorry for the inconvenience, but things like this happen with all manufacturers.