09-06-2007, 12:19 AM
hi Engineer this Quetion for you please give the answer. When referring to AC induction motors FLA what mean ?
Jamal
Manchester
Latte
09-06-2007, 12:26 AM
FLA Is Full Load amps, simple enough but then you might hear also SFA Service factor amps. i wont even try to explain that one as i dont understand it enough myself, too many calculations
Regards
Raymond
monkey spanners
09-06-2007, 11:38 AM
Also MRA max rum amps, LRA locked rotor amps (starting current, can be checked if you have a peak hold facility on your current clampmeter)
Jon
jamal adam
12-06-2007, 10:10 PM
:Dwhat Brain of system ?
the answer heart of the refrigeration air conditioning is Compressor