View Full Version : R22 alternative
Yogibear
19-12-2006, 12:40 PM
Hi guys,
Just wondering if any of you have heard of RS-52 as an alternative for R22, and if so has there been any joy with it. It is supposed to be a direct replacement and may have been tested on a few DX units. However I would be interested if any of you know if its been used on a flooded system??
Cheers..Yogi
chillerman2006
19-12-2006, 02:25 PM
hi yogibear
RS52 is more commonly known over here as R428a and was designed for low/medium temperature refigeration.
It can be used with mineral/alkylbenzene/polyolester oils
Running pressure's are similar to R502, a little higher than R22
chillerman2006
Yogibear
22-12-2006, 08:44 AM
Hi Chillerman,
Thank you for you input. im just concerned about putting it into a flooded system. Reckon i would rather change to 134a, although i will drop effeciency, but there are ways around that..
chillerman2006
25-12-2006, 08:37 AM
Hi Chillerman,
Thank you for you input. im just concerned about putting it into a flooded system. Reckon i would rather change to 134a, although i will drop effeciency, but there are ways around that..
HI Yogi
i would have thought R407c would be a better option - pressures are higher but like R134a you will need to retrofit the unit
if you like i can email you a complete list of available gases - there uses - compatible oils etc.
chillerman
mac_J
03-01-2007, 12:29 AM
Hi Chillerman
can you email me a complete list of available altenative gases for R22- there uses - compatible oils etc.
Regards JF
Brian_UK
03-01-2007, 12:35 AM
I don't know, JF lurks for over 7 months and then doesn't even say 'please'.
Hi JF, don't be shy now, we appreciate all posters here.;)
How about R417a (Isceon 59) I believe it is a drop in replacement for R22
Argus
03-01-2007, 10:13 AM
I don't know, JF lurks for over 7 months and then doesn't even say 'please'.
...... using an e mail address as a name is asking for spam.......
chillerman2006
04-01-2007, 09:22 AM
Hi Chillerman
can you email me a complete list of available altenative gases for R22- there uses - compatible oils etc.
Regards JF
Hi John
i have just emailed them to you
chillerman
Andy P
04-01-2007, 11:24 PM
HI Yogi
i would have thought R407c would be a better option - pressures are higher but like R134a you will need to retrofit the unit
chillerman
Hi all,
I suspect that the glide of R-407C is too much for a flooded system (about 7 deg C), and I am not aware of any "drop-in" for R-22 that has no glide. However we have done some testing of various ISCEON MO refrigerants in flooded water chillers. If you put ISCEON MO59 into the plant then what circulates is broadly similar to ISCEON MO29, so the performance can be guesstimated using the MO29 data (glide of about 3 deg C). Oil return from the chiller's original rectifier was also fine. I'm not sure that RS-52 would do the same thing so performance might be very poor. As they say in all the best films "There's only one way to find out"!!
cheers
Andy P
The MG Pony
05-01-2007, 07:15 AM
R-290? Environmentaly safe and good chararistics!