Ok Gary,
lets take a typicalpackage rtu with 2 compressor's piped into
evaps. Circuit 1 is the bottom 50 rows, and circuit 2 is the top 50 rows. Am I to believe that one circuit will provide more moisture removal? I mean I would think the greater surface area would
extract more moisture than just half the coil.
This set up is typical of most carrier rtu below 12 tons.

Gary
15-03-2002, 05:18 AM
You added a compressor, Bernie...lol

Gary
15-03-2002, 06:10 AM
Okay, let's see if I can explain this a little better:

Increasing the airflow increases the coil temp.

Decreasing the airflow decreases the coil temp.

A lower temp coil removes more moisture than a higher temp coil.

A bigger lower temp coil removes even more moisture.

If we install a bigger coil, without changing the airflow, we now have a bigger higher temp coil, which will bring the space temp down faster, but will not do much for the humidity problem, and may in fact make it worse due to the shorter run time.

If we then decrease the airflow, we will have a bigger lower temp coil, which will remove moisture by the bucketsful.

Gary
15-03-2002, 10:17 PM
If instead the original compressor remians and so the coil is being starved somewhat but still has the same ADP then the SHR is maintained but, duty is maintained and dt is maintained.

It all kinda depends on how much larger the coil is, whether the compressor can handle it, and how far we reduce the airflow.

Because of the increased surface area, we can drop the ADP further without freezing the coil.

Gary
15-03-2002, 11:24 PM
So larger coil, slower air but same SST results in reduced ADP and SHR affecting increased moisture removal and of course reduced sensible duty.

And if we want NOT to remove moisture, we shrink the coil and pump up the volume. :)

herefishy
15-03-2002, 11:39 PM
I disagree.....

If you want NOT to remove moisture, you increase coil surface area, in order to decrease TD (increase SST) yet maintain required capacity at resulting lower TD.

I suggest, forget the airflow rate. That factor is inherant in the unit cooler capacity rating. You select air velocities according to the application.... but if you're going to argue the effect of "changing" airflow... don't go there... because we know what that effect is... we're talkin' factory spec, okay..... not in the feild engineering.

Check your data on floral cooler specs.

herefishy
15-03-2002, 11:46 PM
Marc,

recheck my post.... I changed the exact quote you are referring.

herefishy
15-03-2002, 11:47 PM
I always post and then think... It's just more of a problem now, since WebRam put that damn instant reply window on the screen !

herefishy
15-03-2002, 11:51 PM
I was going through my Witt literature. I noticed that in the evaporator capacity data it indicated

"capacity at 10degF TD.....NOT MTD"

MTD?

Is that what I think it is?

herefishy
16-03-2002, 12:00 AM
Gary... I think you're jousting me.

herefishy
16-03-2002, 12:03 AM
Marc,

I expected a little more than that.

herefishy
16-03-2002, 12:13 AM
you were only hoping that I would explain what I think it is ...... SO YOU COULD NAIL ME TO THE WALL THAT YOU'RE WRITING ON !!

MEAN TD?

please..... don't punish me.......

herefishy
16-03-2002, 12:20 AM
Originally posted by Fridgetech
If you had a pack maintain coil SST and the return air temperature was also maintained, then you slowed the fan speed down, you will see the leaving air temp drop and the TEV superheat drop. But the coil still has the same TD. The return air is constant and the SST is constant but we have slowed the air flow down and must therefore be doing less duty.

I agree you are doing less duty. But you can't slow the fan down, and all perameters stay the same. The TD is not going to stay the same, because the coil temperature is going to drop.

I think you're just trying to take up my time.:p

Gary
16-03-2002, 12:50 AM
Dang, I come back from dinner and you guys have filled two pages. And now you're having controlled dreams. LOL

Dan
16-03-2002, 01:02 AM
In answer to bernie's question regarding a two compressor split faced evaporator, I think you would get more dehumidification from operating only one of the coils simply because, as Gary suggests, run time. We find the same phenomenon in stores that have oversized A/C units, high humidity and cold dry bulb because temperature is too rapidly satisfied with both coils operating.

Turning both stages on will withdraw more moisture for the short time the units run, but you will get more latent heat removal in the long haul by operating only one slab, or a/c unit, especially when one is controlled by a humidistat as well as a thermostat.

Gary
16-03-2002, 01:06 AM
Dan would love this conversation. :)

Manufacturers are re-thinking as we speak...lol

I was thinking more along the lines of desert A/C, but okay, let's consider floral cases.

We have two considerations, here. The humidity of the air and the humidity of the product. The product needs high humidity and minimal airflow.

Keeping in mind that this is not my area of expertise, as I understand it, the latest strategy is big coil, low airflow, quick pulldown and re-humidify.

bernie
16-03-2002, 01:14 AM
well that in fact is the argument Ive been having with my boss for awhile now. SO its true, size dosent matter.
What if we add 10%fresh air thru that same coil?
Its a 12 ton machine on a 7 1/4 ton load. The temp swings are rapid. on an 80F day I can drop the temp in the building 10F in 45 minutes. I was considering the RAWL device as I believe its called to solve my problem.
I converted the drive package down from 6000 cfm to 3900 cfm, and dissable 1 compressor.
Im sure when It gets hot again Ill need anither couple of tons,
this is why im considering the above mentioned.

Gary
16-03-2002, 01:14 AM
Speak of the devil...lol

Gary
16-03-2002, 01:26 AM
What does the RAWL device do, Bernie?

Why not disable the second compressor with a humidistat? Bring it back on when the humidity drops?

Dan
16-03-2002, 02:01 AM
Dan would love this conversation.

LOL. I miss one day and there are 40 new posts! I think what Gary was specifically alluding to was what competing theories even Hussmann apparently has to reduce humidity in fan coil service meat cases.

The old theory was to operate with an EPR with a thermostat either as back up or as the primary control and the EPR to keep suction pressure as high as possible. The goal being to maintain desired temperature with highest humidity.

Then a few years ago, the thinking seemed to change. That higher humidity can be maintained by letting the evaporator run colder and cycle a suction stop solenoid for best humidity/temperature control. This thinking follows the line that you refrigerate the case quickly and use the off-cycle to rehumidify the case. An interesting paradox, eh? It is perhaps design and application specific, but for product life, the latter seems better. It would likely further apply to a floral cooler.

The EPR has a lower rate of dehumidification, perhaps maintaining 75 to 80% but an increased run time (often 80%) The t-stat and solenoid will have a 30 to 40% run time, even though RH drops to 50% during the run time. But RH rises to 90% during the off-cycle.

I would hazard that the difference between a floral cooler or meat case operation compared to a/c operation is that there is a greater effect of rehumidification during the off cycle in the refrigeration applications than there is in an a/c application... perhaps attendant to the relative size of the evaporator to the space being conditioned. This might affect a ratio of runtime versus off-time as well as re-evaporation surface during the off-time.

Very enjoyable thread, fellows.

bernie
16-03-2002, 06:20 AM
It is my understanding that the RAWL device will allow be to run that other 6 ton compressor and it will by pass enough hot gas
make up for the drive change I made to the system. While at the same time give me the extra btu's I need on the warmer days.
From what Ive read it will unload down 1 ton equivelant capacity.
This is a pet project of mine. Our company has never tried this before but we do have some latitude for experimenting.

Gary
16-03-2002, 01:54 PM
I'm not sure I understand the A/C problem.

I'm assuming the goal is to increase dehumidification, hence the airflow reduction and disabling the second compressor. Is this correct?

Did making these changes solve the humidity problem?

Did these changes cause other problems?

For what purpose are we considering HGBP?

bernie
16-03-2002, 04:33 PM
Marc I havent had time to read your post yet, Im off too work.
ON the surface it looks very imformative.
OH, its Bernie Glasgow from Chicago Illinios.

Prof Sporlan
16-03-2002, 05:19 PM
Were's the prof these days?
Hes lurking somewhere
He's been in DC giving a presentation at the ARI hvac intructor's workshop..... now he's trying to catch up on all these damn posts.... :)


Lol, lets all phone the Prof at the same time, ready... 1.... 2..... 3!
No need, you've all got a handle on this problem... :)


The prof might hate me, but zp charges should only be used when a manufacturer intentionally slights the motor size for the displacement.
The Prof doesn't mind.... :) In fact, the 'Z' charge is the preferred charge if the compressor can handle the pulldown requirements. The 'ZP' charge has an MOP to limit pressure at the compressor, but the charge will migrate if the head becomes colder than the sensing bulb. The net effect of using a 'ZP' charge is it will slow the pulldown of the box or case temperature, and in doing so it will reduce the load on the compressor.


This equipment is less than 6 months old,
the element is a kt 43 zp
I have also had problems with the 53 elements
The #53 element is a lerger sized element. Perhaps you may be seeing more migration issues with it. Also, you can expect to see more charge migration problems with an internally equalized TEV with a 'ZP' charge, than with an externally equalized TEV. With an internally equalized TEV, you have the underside of the valve diaphragm exposed to evaporating temperature.

80 more posts to go.... :)

bernie
16-03-2002, 07:36 PM
I'm not sure I understand the A/C problem.
The problem is simple, I have a commercial office space that reqires 15 tons of cooloing. This would be split up bewwen 2 rtu
each 7.5 tons
Problem is I have each unit is 12 tons for a total of 24 tons.
To further complicate the issue This building utilizes carrier vvt
control and damper system with automatic changeover betwwen heating ang cooling demands.
The run times for the air conditioning are so short in duration there isnt sufficient run time for dehumidification and with an open ceiling design the excessive air velocity just rains down on the employyes.


I'm assuming the goal is to increase dehumidification, hence the airflow reduction and disabling the second compressor. Is this correct?
Yes, and no. By reducing the total cfm output The system runs for a longer duration and has eliminated the rapid temperature swings and has made the winter months quite comfortable. This change was implimented in late december 2001. I have yet to determine the effects of high outdoor amients on this this change, thus the purpose for this discussion.


For what purpose are we considering HGBP?

If I end up needeing that other compressor due to humidty levels that are unacceptable once the weather changes, Ill need to be able to use that 2nd stage compressor with out undoing the drive change I made to the machine. This is why Im intrested in HGBP> This is all in an effort to save the customer the cost of replacing the roof top units as they were just installed in 1993.

Gary
16-03-2002, 08:14 PM
It seems then that the ideal would be to bypass hot gas to the distributor on each coil, adjusting it to maintain SST just above freezing, thus minimizing ADP. Then if the total heat removal is insufficient, increase the airflow.

bernie
16-03-2002, 09:10 PM
Please, Ill have to plead ignorrant. What is ADP? Im sure I know what it is if I knew what you meant. :>)

Gary
16-03-2002, 09:19 PM
ADP = Apparatus Dew Point

The lower the ADP, the more moisture is removed.

bernie
16-03-2002, 09:28 PM
ok lets explore that a little furhter to ensure I ifact understand what you mean.
In our case the apparratus is the evaporator coil.
The dew point is when the temperature of the coil is optimum
for extracting moisture from the air passing thru it.
So I would assume that a slower fan speed would reduce the evaporator temp thus lowering the adp?
Is this thought process correct?

Gary
16-03-2002, 09:33 PM
You got it. :)

bernie
16-03-2002, 09:50 PM
I really like your idea of splitting up the duty between both compressors by passing hot gas into both the evaporator rather than just one.
Wit air conditioning return gas temps are higher and acceptable up to 65F in some cases.
Im going to have to get the data for this machine and really scrutinize it to insure I size this properly.
Of course I have to entertain the liquid injection aspect of it also,
I have to find that web site again about that RAWL device.
It so simple to install, there is alot less piping to do. Its an all in one from what I remember.

bernie
16-03-2002, 09:56 PM
Hello marc,
Could you provide me with what Lmtd means? Im sure I know what it is if I knew what you meant. :>)

Gary
16-03-2002, 10:05 PM
I'm thinking to complete the picture, we need to know what brings in the second compressor. If it is brought in by suction pressure, we could have both compressors running regardless of load.

bernie
16-03-2002, 10:06 PM
Well My guess is it would cut in to its product line but more
importantly the rawl is a one size fits all concept.
Ofcourse those in the field know better and I think thats why sporlan recommends the use of a DVB and a desuperheating
TEV to achieve more accurate results that are application specific.

bernie
16-03-2002, 10:12 PM
I'm thinking to complete the picture, we need to know what brings in the second compressor. If it is brought in by suction pressure, we could have both compressors running regardless of load.

In this case its the system demand as it is communicated to the monitor thermostat. Either a large difference in space temp and set point, or the vvt system monitors duct temperature and stages the compressors arrodingly.
This system is set to maintain 50 discharge air temp, if we are above that temp for say 5 min or so during a call for cooling the 2nd stage will be turned on.

bernie
16-03-2002, 10:22 PM
Can someone post a link were I can download a goog coversion calculator? This k(kelvin) C (Celcius) make it difficult at a glance to keep up. Im terrible with algebra:>)

Gary
16-03-2002, 10:31 PM
That control strategy should work well with the HGBV on both coils. :)

Gary
16-03-2002, 11:00 PM
I really like your idea of splitting up the duty between both compressors by passing hot gas into both the evaporator rather than just one.

If either of the coils do not have hot gas bypass, that coil could freeze because of the reduced airflow, so this must be done to both coils.

The advantage to reducing airflow is increased dehumidification.

The danger is coil freezing.

The disadvantage is reduced system capacity. But since this unit is oversized, this does not apply here.

Mike Hopkins
17-03-2002, 01:14 AM
These units we are talking about (like to have a model #)
are most likely of the horizontally split coil. I have some of them in service and have in some applications had to set them up with controls so that either circuit could run if one failed, so cooling would not be lost and various critical equipment that needs cooling starts shutting down and all hell breaks loose with the loss of production and more money down the tubes than it would cost to buy dozens of new units. What I found was that if the top coil ran without the lower coil was that any dehumidfying done by the top coil was re-evaporated by the lower, offline, dry coil, no condensate running out the drain eh! No latent cooling but enough sensible to keep the cooled machinery on-line, though it felt a bit wet in the space. If I had to sit in there for 8 hours doing office duty I would be miserable. Bernie probably has the carrier rooftops with 06D compressors and horizontal split coils? How many unloaders? How many heads or cylinder pairs? These units are slapped up on rooftops by unknowing engineers by the dozens and frequent short cycle and humidity control problems crop up rather readily for the mechanics to deal with. They size them for worst case loads and don't worry too much about about what happens when the load is not so great and we go past the unloading capacity of the machine and get into the short cycle or no latent removal zone. Get some model #'s up on here and let's look at exact original design and go from there, maybe a control scenario could be worked out to tweak cycle times and or off cycle time to maximize latent load control.
Mike Hopkins

bernie
17-03-2002, 11:49 PM
Carrier M# 48hjd014
Nominal capacity 12.5 tons
compressor 2 RECIP
refrigerant type R-22
Circuit 1 9# 8o.z.
Circuit 2 9# 5o.z.
condenser fan 2 propellar @ 22" diameter
evaporator fan centrifugal 15"x15"
Nominal cfm 5000 @ 942 RPM @ 0.2 extrnal static(in. wg)

total face area of evaporator 11.1(sq ft)

Mike Hopkins
18-03-2002, 12:41 AM
An 014, you can throw unloading out, both compressors will be can recips. Either 1 or both compressors or nothing in between.
Carrier did have an option on those units called a moisturemiser.
Basically they called it a subcooling coil which was placed on the leaving side of the evap and took hot gas off the compressor instead of using the regular air cooled condenser to reheat the leaving air and reduce humidity without using electric strips to do the job. You may look to see if the units could be equipped with that option and field install it. Control would be by humidistat and bring unit on in reheat mode running 1 compressor and auxilliary condenser, if set up right you could put airflow back to original.
You could still run wide open straight AC when the load hits in the summer. Probably similar to the RAWL device but designed for the unit by the manufacturer.