View Full Version : New install with pump down??



justchillin'
23-09-2006, 09:23 AM
Hi I am supposed to be fitting a remote unit to a new caravell chilled display,now i have been working on air con for the past 5 years and havent installed fridge for some time.
My only worry is do I use a pump down system or put a contactor on the outdoor and wire the control through the controller.
Also what is the best condensing unit to go for, a unit with everthing all included like a L'unite Silensys are a normal unit and fit it all on site.This system is on R404a and is evaporating at -7 and has a 3 kw coil.Thanks for reading

Mark
23-09-2006, 09:46 AM
Hi Justchillin'

Post more details on site requirements-a standard pump down system is one of the easiest and effective methods.

Kind regards Mark:)

Andy
23-09-2006, 11:42 AM
Hi Justchillin'

Post more details on site requirements-a standard pump down system is one of the easiest and effective methods.

Kind regards Mark:)

With pumpdown no control wiring is need from indoor to outdoor:) just a mains to the condensing unit isolator.
We use maneurope condensing units on such applications and find them relyable in service.

Kind Regards Andy:)