Log in

View Full Version : High Disc Temp



road31
14-09-2006, 02:02 PM
I am fighting a high disc temp what causes this and what should I do. This is on a 1000 ton york chiller.

ROAD

Mauro
14-09-2006, 02:43 PM
mornig, Road 31
Which or modelo I give seu compressor? Which pressao de trabalho? which or superaquecimento? é resfriado to ar ou to água?
Mauro

Mauro
14-09-2006, 02:46 PM
sorry;
Which the model of its compressor? Which pressao of work? which the overheating? is cooled to air or the water?
Mauro

road31
14-09-2006, 03:11 PM
It is a screw compressor model ys nn nn s7 york.

chilled water and tower water for condensor side.

road31
14-09-2006, 03:13 PM
It shuts down on high disc temp

Mauro
14-09-2006, 03:28 PM
sorry, friend
but I will not be able helps it therefore I do not have much esperiencia with this type of comporessor, enters in the site of “York”.
mauro

NoNickName
14-09-2006, 03:40 PM
Is it a centrifugal chiller? What are the superheating (if not flooded evap) and subcooling?

road31
14-09-2006, 06:44 PM
its a screw compressor, would this happen at a low load and also if air temp was low

refteach
14-09-2006, 07:39 PM
At low flow rates you are not moving alot of refrigerant through the compressor and you are relying on the oil to cool the compressor, what is the oil temperature when it goes down? It could be either your oil temp is too high (what type of oil cooling?) or your oil injection flow rate is restricted.

NoNickName
15-09-2006, 08:47 AM
At low load, screw compressors are prone to high discharge temp. Unless superheating can be reduced so that discharge temp can reduce, I would suggest liquid injection to cool the windings.