I,ve been having head pressure problems with searle condensing units
Model no NCU 84-3LS
The fan speed controller sensor connected to one of the condenser bends is secured with a rubber band which streches with the heat, lifting the sensor of the bend.Once cable tied securely problem sorted.Just thought I,d share my findings with you.
Regards Bernard:)