Hello
i have a chiller Sanyo SCP-AR301E8
fault code E41 and E02
I cannot find something on the internet
Who can helps?
Greetings Fernando

TrevH
13-06-2023, 05:31 PM
Maybe the customer will have the op. and maintenance manual? or it might be inside the chiller?

Failing that .....phone Sanyo agent/supplier who should have access to fault codes or tech support number

While you wait perhaps check the basics, good voltage on phases, flow switch/meter on hydronic side, if there is sufficient charge for LP switch/sensor to operate etc.....

Loops
03-08-2023, 12:23 PM
Hi csrbv,

If you are still after information I have install manual and service manual and parts list for this Sanyo Chiller.
Let me know if these would be useful to you.

Regards
Loops

Loops
03-08-2023, 12:29 PM
Oh and the E41 is poor water flow - you should be getting 5.33m³\hr
I can't find anything on E02 error code.