PDA

View Full Version : Blast Freezer Interstage cooler



william.wye
20-04-2023, 05:40 AM
Can someone please explain the the purpose and the function of an interstage cooler on a blast freezer.

Peter_1
20-04-2023, 07:12 AM
Show a schematic what you mean? I think compressor ratio will otherwise too large

NH3LVR
20-04-2023, 04:44 PM
There are many reasons.
I will stick with using NH3 as an example.
NH3 has discharge temperature issues at high compression ratios, particularly with piston compressors.
If you attempt to go from -40F (-40C) suction to 86F (30C) discharge the life of the compressor will be affected severely.
If we split compression into two stages and cool in between we can keep temperatures down to a reasonable level.
There are also energy savings to be had. If we attempt to run a single stage the HP (KW) required at startup is much more than what is needed when the initial high load falls off.
Then there are screw compressors. That is another conversation.

william.wye
20-04-2023, 08:09 PM
Thx NH3 for that. It makes sence to cool the refrigerent.between the stages. was wondering what why a there wasca brach off from the liquid line into the interstage cooler line. It's there to cool the compressed ***** between the staged.

RANGER1
20-04-2023, 09:00 PM
https://m.youtube.com/watch?v=peVAaLIJJ6c

This might help 5.40 minutes into video.

NH3LVR
20-04-2023, 10:00 PM
Excellent RANGER1!
Saved me a lot of typing and Brainwork!

Peter_1
21-04-2023, 08:01 AM
https://m.youtube.com/watch?v=peVAaLIJJ6c

This might help 5.40 minutes into video.

This one is saved on my computer for my students...

RANGER1
21-04-2023, 09:06 AM
Excellent RANGER1!
Saved me a lot of typing and Brainwork!

Danfoss have a lot of good stuff like this, like the way they show flows & colours.
Seems a lot of other stuff assembling valves, like big ICLX.
Had one not assembled on new installation, so was pretty handy as well.
The hand book is also very good.

https://m.youtube.com/watch?v=emKDl8E1xu4

Connor
09-08-2023, 07:27 PM
Hey,
Certainly! The branch from the liquid line to the interstate cooler serves a crucial purpose. It helps cool the compressed ***** between stages, (https://youtubvanced.org/) optimizing efficiency. This cooling minimizes potential heat buildup and ensures smoother transitions, enhancing overall system performance.

udit01
29-01-2024, 06:11 PM
In the realm of industrial refrigeration, the term Blast Freezer Interstage Cooler likely sparks thoughts of efficiency and precision. Imagining this equipment suggests a critical role in rapidly cooling products between stages, ensuring optimal temperature control and preserving (https://whatsgbpro.org/) the quality of perishable goods during the freezing process.

frank
29-01-2024, 06:46 PM
In the realm of industrial refrigeration, the term Blast Freezer Interstage Cooler likely sparks thoughts of efficiency and precision. Imagining this equipment suggests a critical role in rapidly cooling products between stages, ensuring optimal temperature control and preserving (https://whatsgbpro.org/) the quality of perishable goods during the freezing process.

Another nonsense post....I despair

seanf
29-01-2024, 10:13 PM
Another nonsense post....I despair

Is there anything that could be added to the member registration form/process?

jannickz
27-02-2024, 02:06 AM
The primary purpose of an interstage cooler in a blast freezer is to significantly improve the overall efficiency of the refrigeration system.