22-02-2023, 03:12 PM
Hi folks,
Wonder if anyone has any experience of doing central control on multiple Panasonic splits? I'm not particularly familiar with Panasonic and seem to have hit a brick wall.
For context, there are 6 splits over this building; PZH2 outdoor units; it's 1:1 outdoor to indoor units, each indoor unit having its own CZ-RTC5 controller.
Have got a CZ-64ESMC3 central controller (CZ from this point!) to install - there is 2 core shielded wire running between each indoor unit.
The wiring instructions in the installation manual for this unit get a bit ambiguous when it comes to interunit wiring with the indoor/outdoor units.
With u1, u2 & functional earth linking all units in sequence starting with the CZ, I get E08 UNIT 1-1 errors on each device. At this point, I simplified things and broke it down to troubleshoot:
Started with CZ linked to the first indoor unit only - it assigns the unit and is able to control it. When I add the interlink to the second indoor unit, the E08 errors happen again, CZ not detecting any units.
After this I tried taking the link from the central controller to the outdoor unit first, with an interlink between the first and second outdoor units - same issue.
It is clear that the separate units all have an ID of 1-1, which is obviously conflicting, but I can't seem to get them to assign themselves different IDs, or find a way to do it manually - from the way that the units behave on power up (including the CZ), I'd expect it to do some auto addressing based on what they can detect around them?
Am I way off the mark here, am I missing something painfully obvious?
Thanks in advance for any advice.
Wonder if anyone has any experience of doing central control on multiple Panasonic splits? I'm not particularly familiar with Panasonic and seem to have hit a brick wall.
For context, there are 6 splits over this building; PZH2 outdoor units; it's 1:1 outdoor to indoor units, each indoor unit having its own CZ-RTC5 controller.
Have got a CZ-64ESMC3 central controller (CZ from this point!) to install - there is 2 core shielded wire running between each indoor unit.
The wiring instructions in the installation manual for this unit get a bit ambiguous when it comes to interunit wiring with the indoor/outdoor units.
With u1, u2 & functional earth linking all units in sequence starting with the CZ, I get E08 UNIT 1-1 errors on each device. At this point, I simplified things and broke it down to troubleshoot:
Started with CZ linked to the first indoor unit only - it assigns the unit and is able to control it. When I add the interlink to the second indoor unit, the E08 errors happen again, CZ not detecting any units.
After this I tried taking the link from the central controller to the outdoor unit first, with an interlink between the first and second outdoor units - same issue.
It is clear that the separate units all have an ID of 1-1, which is obviously conflicting, but I can't seem to get them to assign themselves different IDs, or find a way to do it manually - from the way that the units behave on power up (including the CZ), I'd expect it to do some auto addressing based on what they can detect around them?
Am I way off the mark here, am I missing something painfully obvious?
Thanks in advance for any advice.