Im having issues with a City multi PURY P250 YMF.

It seems to run in heating mode fine - but when it runs in cooling it trips out on HP straight away. I suspect that the 4 way valve may be stuck? how can I prove this - and if it needs to be changed - how big a job is that?

thanks

narkom
01-10-2022, 09:52 AM
I would think of the check valve CV1.

BROBERTSON
04-01-2023, 12:56 AM
Thanks, I intend having a look at this in the next few weeks- before we need To go in to cooling mode. Apparently Mitsubishi do a check valve repair kit - you ever overhauled one ? I have units either side so only have access from the front and rear

narkom
04-01-2023, 11:53 AM
I don't think any check valve is reparable, it supposed to be changed.
BTW, besides CV1, the CV7 check valve could be a problem. This valve works in cooling mode only.https://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=16178&stc=1