View Full Version : low duct temperature



Rick H
14-06-2022, 03:23 AM
I have a 2.5 ton split unit. New evaporator last year. It all worked fine until now. However now I cannot get lower than 65 degrees out of the duct anywhere in the house. This was in the 50's before.
Suction 125
head 280
Condenser unit is about 4 years old. Seams to be working good.
I am at a loss.

Thanks

Rick

frank
14-06-2022, 07:35 AM
Pressures are meaningless without knowing what refrigerant you are talking about.

Other parameters such as air entering, air leaving, room temp etc. also help.

Rick H
14-06-2022, 07:14 PM
Pressures are meaningless without knowing what refrigerant you are talking about.

Other parameters such as air entering, air leaving, room temp etc. also help.

Sorry r410

superheat 10-13
subcooling 10

air into evaporator 73
room temp 73
temp at evaporator {little temp lead inside) about 53

of course temp outside is 95-100

frank
15-06-2022, 06:21 AM
I would suspect that you have a refrigerant shortage.

The only way to tell is to recover and check the amount against the nameplate charge.