View Full Version : Airco hose question



HvacNewBee
28-03-2022, 11:34 PM
Question to the ac installers: suppose I would connect my new ac split unit with hoses like the one in the attached picture, would I still have to isolate the hoses to prevent them from getting wet/condensed or will the rubber hose isolation be enough? Thanks a million.

16083

Brian_UK
29-03-2022, 12:11 AM
Well, where do we start?

The hoses are not designed for long time permanent usage with variable operating temperatures.

The hose bore is insufficient to handle the refrigerant flow.

The suggestion demonstrates the lack of competent training by the originator of this hare brained idea.

The hose connectors do not comply with current regulations.

frank
29-03-2022, 08:26 AM
Even the picture say's that it a ' charging hose' i.e. a service tool