31-12-2021, 10:26 AM
Hi all,

Just wanted to pick a brain.

Klimac chiller has gone into a contactor status alarm, this had has new controls upgrade by Airedale controls, so new wiring and some sensors but existing equipment.

Changed the motor protection module and fault disappeared, however has returned, oil is present, no HP trips etc.

Any ideas on possible places to look please?

Brian_UK
31-12-2021, 10:32 AM
I have no knowledge of your unit but as it has had new controls and I assume controller too, are all of the new parameters set up suitable for the existing kit?

Stretch79
31-12-2021, 03:21 PM
Hi Brian

Attended today for a call out on it.

Comp running really hot and casing too hot to touch.

Fault was heat temp sensor due to this. High discharge pressure and temps.

Fridge, oil all looked ok, condenser coils heavily blocked

Brian_UK
01-01-2022, 12:02 AM
Can't beat the mark one eyeball for potential simple fault causes.

Stretch79
01-01-2022, 12:13 AM
Yeah thanks mate.

It’s nice when it’s the simple things. Think sometimes I over complicate stuff and go to deep lol

Brian_UK
01-01-2022, 12:40 PM
Yeah thanks mate.

It’s nice when it’s the simple things. Think sometimes I over complicate stuff and go to deep lol
If it helps to sort the problems then it pays off.