View Full Version : Oil jumping in separator
shaaf
04-11-2021, 06:11 PM
Hi Everyone
Hope you are all doing well
Here is one illusion that oil jumping in oil separator (gea)
What can be caused?
Awaiting your kind words.
Following link
https://youtube.com/shorts/_lxXlMONXZM?feature=share
Thanks in advance
shaaf
04-11-2021, 06:15 PM
I'm trying to upload a video but error occurred everytime
RANGER1
04-11-2021, 08:23 PM
Hi Everyone
Hope you are all doing well
Here is one illusion that oil jumping in oil separator (gea)
What can be caused?
Awaiting your kind words.
Following link
https://youtube.com/shorts/_lxXlMONXZM?feature=share
Thanks in advance
Shaaf,
Link okay, try running oil level a bit lower, like 25% to 50 % see if better.
Assume new package.
cricri
05-11-2021, 10:02 AM
Shaaf,
what is your refrigerant?
shaaf
05-11-2021, 10:49 AM
Shaaf,
what is your refrigerant?
NH³ Ammonia
cricri
05-11-2021, 11:29 AM
Normal oil level should be 1/3 to 1/2 of glass.
This is not the issue.
It seems that the is ammonia in the oil, what are disch pressure, disch temperature and oil temp, room temperature?
Must be liquid ammonia in oil.
Nothing to be upset.
It will be back to normal after some running.
shaaf
06-11-2021, 02:12 PM
Thanks to everyone
Problem Sort out.
Actually it was standby unit we operate it in rare cases. Once Gea engineer PM done and that time he done some settings.
Oil return from PHE timer setting was changed. It was opening for 30 seconds and delay time was 10 seconds. Instead of oil there was liquid with oil. Liquid was hurting.
Anyhow good experience