Rosomaczek
04-11-2021, 03:30 PM
Hi,
I have problem with heating in this outdoor unit toshiba rav-sm2804at8-e. It working in cooling mode but do not work in heating mode. There is no errors, only one in memory P05 when I checked it on PCB board.
Thank you for help in advance.

frank
04-11-2021, 05:01 PM
Carefully check the outdoor unit main printed circuit board and see if Jumper J808 has been cut

Rosomaczek
05-11-2021, 07:34 AM
Carefully check the outdoor unit main printed circuit board and see if Jumper J808 has been cut
Jumper J808 was not cuted.

frank
05-11-2021, 10:18 AM
On the remote controller press Test + SET + CL for 4 seconds

Sroll down to the 'OF' setting and let me know what the Value is.

Tayters
09-11-2021, 04:39 PM
Some splits have a small PCB near the interconnect with some DIP switches on which gets corroded.
Try unplugging this from the main PCB.
One of those switches selects no heat function which might be your issues. If it is you can just leave it unplugged.

Cheers,
Andy.