View Full Version : Daikin Convenipack Test mode?



CHEMASKBG
16-07-2021, 01:25 PM
Anyone knows how to enter the test operation mode on a Daikin CVP (Convenipack) or Zeas?

I have tried to press the testbutton on the outdoorunit for 5 sek but no success.

:confused:

Brian_UK
16-07-2021, 07:00 PM
Have you followed the instructions within the installation or service manual?

Does your system include a booster unit?

frank
16-07-2021, 09:32 PM
Here you go. https://manualzz.com/doc/901740/daikin-lrleq15ay1-e--service-manual

See page 71

CHEMASKBG
17-07-2021, 11:57 AM
Have you followed the instructions within the installation or service manual?

Does your system include a booster unit?

I've checked both the service manual and installation manual. Maybe I have the wrong ones? The things I found about self test was with a controller. But I don't have one. I was more thinking how to start the test with the buttons on the outdoor unit.

I have some trouble with the cvp. It gives a warning of protection device. Sometimes. I have measured all three compressors and they are fine. I have changed both pressure sensors and thermistors. No success.

Yes it has one booster.

CHEMASKBG
17-07-2021, 11:58 AM
Here you go. https://manualzz.com/doc/901740/daikin-lrleq15ay1-e--service-manual

See page 71

It's not saying how to start the test? I'm so sorry. Can't find it.

frank
17-07-2021, 04:25 PM
Page 71.
Section 5.6
Item 2.
Turn RUN switch to ON

CHEMASKBG
19-07-2021, 08:05 AM
Page 71.
Section 5.6
Item 2.
Turn RUN switch to ON



Ok. I thought there was a more extended test feature. On Zeas machines there are apparently.