16-07-2021, 05:19 AM
I got a freezer that can go to maximum -15 degrees now.

Would it be able to go to -20 degrees if I change the thermostat max settings?

mbc
16-07-2021, 07:13 AM
Hi
Main thing is that .
But to give you right answer need to know more about your system
Type of refrigerant and compressor.

Rob White
16-07-2021, 10:26 AM
.

Minus 15 for a freezer is unusual.
Minus 20 is more like the normal.

Are you sure this is a freezer?

Rob

.

Brian_UK
16-07-2021, 01:01 PM
Did it go to lower temperatures before now?

What is ambient temperature around the freezer?

Has anything changed since first installation?

Is compressor running still at -15 or is thermostat still calling for compressor?

puansingye
17-07-2021, 06:09 PM
No, it did not go below -15.

Compressor model: L76CZ1
Refrigerant: R134A

Understand that R134A is not able to go to lower temperature. Must be R404A, correct?

Rob White
31-07-2021, 09:56 PM
.

If it is this comp then Minus 23 evap temp equates to about minus 13 case temp.

https://www.womacool.com/productinfo/284992.html


So if it is at minus 15 then you are at the limits of the comp.

Rob


.

skarrs71
18-08-2021, 08:07 PM
On 134a comp would need to run in vac on suction to achieve -20, which is never a good idea unless it is a special design, for low temp should be 448A, 449A, 407A or F, but on a 134a system may well require different pipework sizing, would probably be better to replace with a properly specified system.