knighty
21-06-2021, 08:35 PM
I have a 15hp system I need to move from a walk in freezer into a shipping container... but the evap won't fit
new blast freezer plan means I need evaps at the far end of a container blowing down the length
compressor is bitzer 4PCS-10.2Y https://www.hosbv.com/data/specifications/12668_4PCS-10.2Y-40P.pdf
I'd love to use Kelvion Searle KME KME95-6L evaps - each container will have one of the above 15hp systems and a 2nd 7hp system which already uses those evaps - makes it much easier for me stacking the evaps if they're all the same
page 8 here https://www.hosbv.com/data/specifications/5471%20-Searle%20KM140-6%20E.pdf
says evaps are rated for 12.50kw on 404a at 8'C deltaT
condensing units rated for 20kw at -20'C evap
those look to match up ok to everyone here?
I should do with a push in the right direction for picking TEVs and orifices
I'm keen on electronic expansion valves... but the more I think about it the more I think it's just more to break down in the future?
new blast freezer plan means I need evaps at the far end of a container blowing down the length
compressor is bitzer 4PCS-10.2Y https://www.hosbv.com/data/specifications/12668_4PCS-10.2Y-40P.pdf
I'd love to use Kelvion Searle KME KME95-6L evaps - each container will have one of the above 15hp systems and a 2nd 7hp system which already uses those evaps - makes it much easier for me stacking the evaps if they're all the same
page 8 here https://www.hosbv.com/data/specifications/5471%20-Searle%20KM140-6%20E.pdf
says evaps are rated for 12.50kw on 404a at 8'C deltaT
condensing units rated for 20kw at -20'C evap
those look to match up ok to everyone here?
I should do with a push in the right direction for picking TEVs and orifices
I'm keen on electronic expansion valves... but the more I think about it the more I think it's just more to break down in the future?