Log in

View Full Version : Mitsubishi par-ct01maa-sb



ronaldo9
26-05-2021, 08:39 PM
For the love of god does anyone know how to set the auto mode to single set point on a par-ct01maa-sb? There are only two auto settings on the controller and neither of them effect the auto set point .

Cheers

Brian_UK
27-05-2021, 12:06 AM
Most efficient controls will have a dead band to prevent hunting, are you trying to not have that option?

ronaldo9
27-05-2021, 07:49 AM
Cheers Brian,
Essentially they want units locked into auto mode with a temp range between 19 and 24 . For simplicity I would prefer if the user didn’t have a max and min set point and instead have a single set point within the 19 to 24 range. As it stands I cannot get the controller to use a single set point in auto mode .

frank
27-05-2021, 08:19 AM
Here's a link to the manual https://www.google.com/url?sa=t&source=web&rct=j&url=https://library.mitsubishielectric.co.uk/pdf/download_full/3673&ved=2ahUKEwjH4YDhp-nwAhXN5-AKHS4sABYQFjAFegQIExAC&usg=AOvVaw18Lzqugy4fqyhyWG6L-zZe

The Auto mode gives dual setpoint (cool/heat) then you lock the controller