PDA

View Full Version : NH3 against R22



skyboy6142
03-04-2021, 05:43 PM
Dear friends,

I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?

Thanks in advance.

RANGER1
03-04-2021, 08:16 PM
Dear friends,

I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?

Thanks in advance.

Skyboy,
If it was a Mycom 200VLD compressor - 10 deg C sst 35 deg C sct

Nh3 821kw 203kw absorbed power
R22 792 kw 209 kw
R22 much denser refrigerant

So same in this case

https://agilityrefrigeration.weebly.com/information/comparison-between-refrigerants-ammonia-vs-*****

Josip
03-04-2021, 09:11 PM
Hi skyboy6142,

Dear friends,

I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?

Thanks in advance.

something from your neighborhood ...
https://agilityrefrigeration.weebly.com/information/comparison-between-refrigerants-ammonia-vs-*****


Best regards, Josip

mbc
04-04-2021, 01:02 PM
Hi
In low temperature R22 has more efincy than NH3

skyboy6142
05-04-2021, 04:35 PM
Thanks from all of you

PEPELEBU
13-04-2021, 02:31 PM
Skyboy,

With an open piston compressor no cooling at all. At same regime -15 ºC / +35 ºC, both @ 1,000 rpm
R22 - 335,2 kW @ 117,7 kW absorb power.
R717 (NH3) - 335,5 kW @ 106,3 kW absorb power.

And then discharge temperature on R717 will be much higher.

Just remember GWP of R717 = 0, R22 = 1,810...

I hope with this you don't even keep thinking on using R22.

Take care...

D