View Full Version : Daikin vrv e3 problem



Vivek
09-01-2021, 04:18 PM
Hi all, Daikin vrv 6hp, showing e3 error,gas not come out from the outdoor unit and compressor start up 2 amps suddenly it taken 15 amps, compressor heat up more.high and low pressure sensor replaced,eev replaced, compressor both new, HP &lp switch ok but still e3 error detected, some one know what is the problem, pls help

nike123
10-01-2021, 10:29 AM
It looks like you have restriction in refrigerant flow from compressor. Reset the unit and confirm that you realy have too high pressure with measuring high pressure during compressor startup untill error is present again.

If not, and assuming you have OK sensors, then PCB is faulty.

Does error E3 is present in both cooling and heating mode?

Vivek
10-01-2021, 01:25 PM
Yes sir, both side same problem , control pcb ok , Thx your support.

nike123
10-01-2021, 11:33 PM
You did not confirmed that you actually measured high pressure.

Vivek
11-01-2021, 04:42 AM
Hi ,I finally found its 4way valve defective,
fault rectify, thanks your response.