PDA

View Full Version : UNISAB II strange behavior



Josip
06-08-2020, 11:16 AM
Hello to all!

Recently we faced some problem with UNISAB II.

Compressor with installed unit stopped within different
working time after start (2 minutes, 20 minutes, 1hour+ or even after 2hours)
there is no pattern or we do not see it ...:confused:

So, compressor is running and suddenly Unisab display went black
(like switched off) and within same second restart ... of course compressor
is stopped and must be restarted.

Strange thing is that we do not have any feedback alarm ...
not within UNISAB neither on PLC.

Maybe some of you faced similar problem with UNISAB II
and can give some useful advice ... the last exit is to contact SABROE,
but that is not easy because they forward those questions to nearest
representative .... and then .... not sure what ;)

Thanks for your time and effort.

Best regards, Josip

AKI
06-08-2020, 12:14 PM
Hi Josip, I have similar problem.
You need to change main BIG board or like Sabroe sad RELAY PRINT.

best regards
Predrag

josef
06-08-2020, 08:31 PM
Friend,
he had about the same problem in the past, he replaced the entire front panel and it was OK.

Josef

Josip
06-08-2020, 09:51 PM
Hello Predrag and Josef

Thanks a lot for your answers.

Best regards, Josip