Log in

View Full Version : TXV Icing Up



adijtap
12-07-2020, 07:42 PM
Hi All

I have two undercounter fridges, both sharing one condenser.

A few weeks ago, one of the fridges TXV started to freeze heavily. I allowed it to thaw, and restarted the fridge. Within 15 minutes it was a solid ball of ice again. I switched the fridge off and left as it wasn’t a desperate repair. Last week I was called to look at the other freezer on the same condenser and found the exact same thing happening.

I plan to reclaim tomorrow and reluctantly swap out both valves and driers, though it’s going to be a real pig of a job. The valve are preset and cannot be adjusted.

Anything I’m missing? I find it a tad too coincidental that both valves are misbehaving.

Thanks in advance

Brian_UK
12-07-2020, 09:58 PM
Short of gas?

TXV strainers blocked?

Filter/driers blocking, check temperatures?

Airflows?

NH3LVR
12-07-2020, 10:26 PM
I would check to see if there was a large Temperature difference across the Drier first. This would explain everything.

monkey spanners
13-07-2020, 09:24 PM
Moisture in the system?

adijtap
13-07-2020, 09:44 PM
Thanks boys

Found the unit with only 400g of a 2kilo charge. Fingers crossed I’ll find and repair the leak tomorrow and fill her back up. See if that makes a difference.

Brian_UK
14-07-2020, 12:11 AM
Yep, correct charge could well make a difference. ;)