View Full Version : Daikin vrv VI



Po65
06-07-2020, 07:38 PM
Could anyone tell me how to clear all auto address set on the system vrv VI and re do the auto address
Thanks

frank
07-07-2020, 11:41 AM
Not done it on the VI but on the III series you press and hold the BS5 reset button for 20 seconds, which takes it back to factory settings.

Power down and power back up (indoor and outdoor) and then it will auto address but will leave you with a U3 error, meaning that you must put it through the Test run to clear the U3