PDA

View Full Version : V-Shape condensers



RODRIGO BR
31-05-2020, 05:51 PM
Hi All,

Is there any recommended rule for V-Shape remote condensers installation?
Is it suitable to install this kind of condenser at the same level or below than the evaporator unit? In all aplications that I've seen, this kind of condenser is installed above the evaporator unit.
At this condition (same level), Is it possible to have issues with liquid and oil trapped in the coil condenser?

Many thanks,

RANGER1
31-05-2020, 08:21 PM
Hi All,

Is there any recommended rule for V-Shape remote condensers installation?
Is it suitable to install this kind of condenser at the same level or below than the evaporator unit? In all aplications that I've seen, this kind of condenser is installed above the evaporator unit.
At this condition (same level), Is it possible to have issues with liquid and oil trapped in the coil condenser?

Many thanks,

Rodrigo.
I think Glenn Moore answered this for you in earlier post.
http://www.refrigeration-engineer.com/forums/showthread.php?50273-Compressor-lubrification-issue&p=328664#post328664
Having a liquid receiver may also help to drain & store excess liquid.

RODRIGO BR
01-06-2020, 12:20 AM
Hi Ranger,

Thanks for your reply.
Yes. Glenn answered about V shape with two coils connected. Much appreciated Glenn for this.
I would like to know also for non coil connected and condenser at the same level than evaporator. I did not find any documentation or manufacturer installation recomendations about this kind of application.

Thanks a lot

RANGER1
01-06-2020, 09:10 AM
Hi Ranger,

Thanks for your reply.
Yes. Glenn answered about V shape with two coils connected. Much appreciated Glenn for this.
I would like to know also for non coil connected and condenser at the same level than evaporator. I did not find any documentation or manufacturer installation recomendations about this kind of application.

Thanks a lot

Rodrigo,
I cannot see any reason why not.
Oil return is the only thing in any system, but mainly problem if under very low loads for long periods.
If piping selected correctly all should be good.
As far as design of plant other things might need to be addressed.
This link maybe useful, or create more questions than answers.

https://www.tranebelgium.com/files/book-doc/20/en/20.aqerykdx.pdf

RODRIGO BR
01-06-2020, 03:38 PM
Hi Ranger,

Thanks a lot for your help and for share this information. Very usefull.

Thanks

RODRIGO BR
05-09-2020, 02:12 AM
Hi,

Just to give a feedback about some informativon I had received from the condenser's manufacturer of this case.
This specific model condenser from this manufacturer, it is only recommended and suitable to install the V-Shape condenser at 1,5m above the compressor's level. Below this height the condenser could retain oil.

Thanks to everyone who helps some way.

Rodrigo