How can we estimate the liquid quantity in a jug, by knowing its pressure and temperature?
Brian_UK
27-04-2020, 02:02 PM
If by jug you mean a refrigerant cylinder then simply weigh it and subtract the tare weight to give the weight of the contents.
nevinjohn
02-05-2020, 12:47 PM
Yeah, but how exactly do I know what percentage is liquid and gas? The PT chart would show the refrigerant within the saturation curve, but how can I estimate the liquid/gas percentage....
seanf
02-05-2020, 02:49 PM
The way Ive seen it done is,
- Find the specific volume of the total contents -
v = Volume of cylinder / Mass of the refrigerant (vapour and liquid)
- Use the refrigerants property tables to find the specific volumes of the vapour and of the liquid at the saturation temp/pressure. -
vg - specific volume of the vapour
vf - specific volume of the liquid
- Find the Quality -
x = (v - vf) / (vg - vf)
- The mass of vapour is then found -
Mass of vapour = (quality) X (total mass (liquid and vapour))
You can work out the rest from that.
The above is given as an example in the book, Thermodynamics: An Engineering Approach, Çengel/Boles, 8th edition, page 129, Properties of Saturated Liquid-Vapour Mixture. More than likely to find it online for free.
Brian_UK
02-05-2020, 03:19 PM
Or, tap the side of the cylinder with a small spanner moving slowly from the base up to the top. When the sound note changes then you have found the top of the liquid.
r.bartlett
02-05-2020, 05:10 PM
This is a test or homework question not a out in the field one :-)
nevinjohn
15-05-2020, 09:27 AM
Thanks a lot guys! I was just being curious whenever I see a liquid receiver. Now it makes some sense :-)
nevinjohn
15-05-2020, 09:28 AM
haha... definitely not in field.
Josip
15-05-2020, 01:47 PM
Thanks a lot guys! I was just being curious whenever I see a liquid receiver. Now it makes some sense :-)
Here you can read a little more all about: ... easy way ... all is within RE forums ;)
http://www.refrigeration-engineer.com/forums/showthread.php?4365-Liquid-receiver
http://www.refrigeration-engineer.com/forums/showthread.php?4436-Liquid-receiver-size
http://www.refrigeration-engineer.com/forums/showthread.php?46172-Volume-of-chiller-liquid-receiver
http://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=14178&d=1466916864
best regards,
Josip
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.