Today I've had the usual "grown man crying because of warm beer" call! The unit is short cycling like it's short on refrigerant (r404). Three months back I thought there was moisture in the system because of massive head pressures but after calling the cabinet and motor manufacturers I found out both parts was delivered to different parts of the country 10 years before the shop even opened. Now this gets better!
We have 20m3 of cabinet space connected with (unnecessary extra 15m) and a total of 30m 1/2" & 1/4" suction and discharge connected to a 3hp motor (which is 4x too big for the cabinets) and I've spoken to the manufacturer who have calculated the discharge is fine but the suction needs swapping out for 3/4"? And there's not one oil trap from beginning to end!!
Any help in untangling this birds nest would be greatly appreciated thanks!
We have 20m3 of cabinet space connected with (unnecessary extra 15m) and a total of 30m 1/2" & 1/4" suction and discharge connected to a 3hp motor (which is 4x too big for the cabinets) and I've spoken to the manufacturer who have calculated the discharge is fine but the suction needs swapping out for 3/4"? And there's not one oil trap from beginning to end!!