29-02-2020, 10:18 AM
hello

I have problem with my ac chiller with my hardware board Same as photo my controller is W3000 controller..

my problem is i have alarm code 211 and 212 is high pressure in circuit 1 and 2,every things in my unit is ok and i check my high pressure is ok and change it by new but still alarm is appear and i connot run compressor.

we I try to change compete hardware board by new no alarm coming because is new board.SO COULD any one help my to to delete this alarm i have now 10 PCB board with same alarm..!!

i have user psassoword is 1234
assitance is 9990
manfactor is 0000009982

also i need super user password ??? can any one give me ???

Munther
29-02-2020, 10:20 AM
15495
15496
15497

frank
29-02-2020, 10:36 AM
Have you reset the trip on the High Pressure switch?

Munther
29-02-2020, 01:18 PM
Have you reset the trip on the High Pressure switch?

No reset switch in pressure switch.. Im sure i dont have any problem in pressure switch

redroge
29-02-2020, 03:54 PM
Have you a photo of hp switches

Grizzly
29-02-2020, 07:08 PM
Try the following.
10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
Good Luck Grizzly

Munther
01-03-2020, 03:08 PM
Try the following.
10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
Good Luck Grizzly


When i tried to press alarm key for 3 second the alarm of high pressure is disappeared but is coming agine after few second.

Every time i have same alarm I just change the complete PCB hardware and every things working good thats means I dont have any problem in my pressure switch.

Around 5 years Im changing around 10 PCB when i have same alarm because i dont have another choose..

Munther
01-03-2020, 03:14 PM
Even When I tried to make pay pass for high pressure switch by installed wire jumber but still the alarm appeared..

al
01-03-2020, 07:39 PM
Is there a second high pressure switch on the circuit that you are missing? Is the motor thermistor in series with this alarm or any other switch?

redroge
01-03-2020, 11:35 PM
Like al said you could have a hp transducer and a Manual reset hp switch it’s not uncommon on some makes of chillers

Munther
03-03-2020, 08:21 AM
15501
15502
15503
15504

frank
03-03-2020, 10:00 AM
Are the pressure transducers 2 wire or 3 wire?

redroge
03-03-2020, 03:08 PM
Press the black button in the middle of the switch that’s the reset

Munther
04-03-2020, 05:57 AM
Are the pressure transducers 2 wire or 3 wire?

2 wire only .. I tried to make wire jumber to paypass but still same alarm ..

As I say before I dont want to change complete board it is so expensive

Munther
04-03-2020, 05:58 AM
Press the black button in the middle of the switch that’s the reset

I tried and no things happen

redroge
04-03-2020, 07:37 AM
After pressing the black button you must do what Grizzly said

frank
04-03-2020, 09:26 AM
Do you have continuity through the 2 wires from the sensor?

Disconnect it from the pcb and measure for continuity with a multimeter - even when pressing the reset button.

Munther
04-03-2020, 09:59 AM
Do you have continuity through the 2 wires from the sensor?

Disconnect it from the pcb and measure for continuity with a multimeter - even when pressing the reset button.

Yes I have continuity between 2 wire ( 0.6 ohm) thats means is Normal close

Munther
04-03-2020, 10:02 AM
All HP switch has been changed by new but still same alarm . I tried today to change complete board PCB and alram is going .. thats mean I dont have any problem in my unit only in PCB and now I have 11 PCB with same alarm .

I think there is some software problem may be

Munther
04-03-2020, 10:05 AM
Try the following.
10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
Good Luck Grizzly

When the alarm is appear I press alarm key button for 5 second and alarm is disappeared but after few second alarm is comming back again.
I Cant run any compressor because this alarm

frank
04-03-2020, 12:37 PM
If you link out the HP switch does your chiller run?

redroge
04-03-2020, 01:28 PM
Have you got a photo of the wiring diagram

Munther
04-03-2020, 06:23 PM
If you link out the HP switch does your chiller run?

No Not running

Munther
04-03-2020, 06:24 PM
Have you got a photo of the wiring diagram

I dont have any wiring dirgram

MeCHanick
05-03-2020, 10:33 AM
I dont have any wiring dirgram

https://www.manualslib.com/manual/491905/Climaveneta-W3000-Compact.html?page=30#manual


Here is the manual, there is a description of the board and connections. Also check the factory settings - at what pressures HP is etc.

Maybe it will help.

[Google translator;)]

frank
05-03-2020, 04:38 PM
What is the Alarm Number on the display?

chemi-cool
06-03-2020, 09:30 AM
What is the Alarm Number on the display?

Look at his first post, AL:211 circuit 1

Munther
08-03-2020, 07:15 AM
Did any body know how to connect my Pc to this PCB
Which software can I use ?? 15507

Munther
13-07-2020, 05:40 AM
Any update ����

nike123
15-07-2020, 01:13 AM
If you have continuity whole time on control circuit related to that alarm, you should take that board to electronic repair shop and tell them to check digital inlet which is related to that alarm. Probably optocoupler issue!

If there is no problem with related digital inlet than it is software issue and you should contact dealer of these units!

nike123
15-07-2020, 01:18 AM
All HP switch has been changed by new but still same alarm . I tried today to change complete board PCB and alram is going .. thats mean I dont have any problem in my unit only in PCB and now I have 11 PCB with same alarm .

I think there is some software problem may be

Are you saying that you have 11 separate chillers with same alarm?

Gibbo
15-07-2020, 03:38 PM
Had a similar problem turned out to be the battery module which feeds the alarm relays if memory serves me right. Caused by low battery voltage but for some reason gives up hp fault.
Gibbo

Munther
13-08-2020, 09:40 AM
Are you saying that you have 11 separate chillers with same alarm?

yes I have around 11 PCB with same alarm :(. there is any software can i connect my board to my lab top and reprogramming the PCB. because Im sure no hardware problem .

Munther
18-08-2020, 05:20 AM
did any boady have any idea how to connect my PCB of chiller to my PC ? there is any software can i use it?

nike123
23-08-2020, 10:02 AM
https://www.carel.com/programming-tools/-/journal_content/56_INSTANCE_i4q5KIMLInKK/10191/54942
https://www.carel.com/product/c-suite (https://www.carel.com/product/c-suite)

But you probably dont have acess to change programing off these PCO-s since Climavenata is making its own software for PCO and it is protected.

Your best bet is to contact manufacturer.

By my expirience, they will never admit that their software is faulty and you will be bounced around like some stupid monkey folowing their instructions. But, maybe you will be lucky monkey!

I usualy install μchiller2 SE in that case, if it is possible.

AlexG
26-08-2020, 02:21 PM
Are you sure that High pressure alarm comes from HP switch but not HP sensor?