View Full Version : Daikin RZQSG71L3V1B No power to indoor



eire1
11-12-2019, 07:52 PM
Hey folks, just wondering if anyone has come across anything similar on a Daikin RZQSG71L3V1B? I’ve an indoor unit that has no power, it’s fed off the outdoor which does have power. I assume it’s either a blown fuse or a faulty PCB? I should add that I had the green LED flashing but no lights on any of H1P to 7. Going back tomorrow with a tall ladder to properly reach and investigate.

martinw58
12-12-2019, 06:05 AM
there are two fuses in the out door unit

frank
13-12-2019, 09:26 AM
Check the High Float switch on the condensate pump. Some installers put the live or neutral through this switch to stop the unit if the pump fails.

eire1
13-12-2019, 10:37 PM
Thanks guys. Found F1 on the outdoor blown. Mini Lime was fine, all indoor connections OK. I found a loose neutral for a pump for outdoor drip trays. I can only assume that this races and blew it. Ran fine for 60 mins once repaired.