View Full Version : Refrigerant compressed air dryer



kaskiris
18-07-2019, 08:08 PM
Dear Colleagues

In a refrigerant air dryer R22, I would like to replace the High Pressure Switch, setting in 28Bar (CUT OUT), with a thermostat and I would like to know at what temperature must be set (CUT OUT).

Thanks a lot.

Best Regards

Brian_UK
18-07-2019, 11:49 PM
Set the same temperature as the original pressure setting was at.

Same switch, different dial.

PaulZ
19-07-2019, 06:54 AM
Hi kaskiris
If it is a HP safety I would not replace it with a thermostat.
Regards
Paul

martinw58
19-07-2019, 08:20 PM
why replace a high pressure safety switch with a thermostat

Brian_UK
20-07-2019, 03:37 PM
why replace a high pressure safety switch with a thermostat
Probably because it has failed and he doesn't have a spare available on the island.

Glenn Moore
20-07-2019, 11:22 PM
This sounds a very strange idea and potentially dangerous . For a thermostat to work, 1) it’s bulb would need to be fitted in one particular position on the system ,2) the bulb would need to be insulated from air movement etc , 3) the thermal lag of the thermostat would need to be taken into consideration.
The thermostat setting would be approx 70 deg C . provided the bulb was fitted to the correct position in the system.
In theory an HP pressure switch will work anywhere on the high side of the system from the discharge pipe through to the liquid line. A thermostat though would only work correctly in one area only .
Perhaps Kashmiris can tell us specifically where he would fit the thermostat bulb as this would need to be correct for correct functionality of the stat to take place.

RANGER1
20-07-2019, 11:35 PM
Is Cyprus really that isolated you can’t get parts overnight, or in a few days?

http://etapol.com/index.php/thermostats-controls

martinw58
21-07-2019, 06:46 AM
dose Cyprus come under f gas regs with regards to working on old R22 equipment

Brian_UK
21-07-2019, 12:57 PM
Is the OP going to reply or are we wasting our time here