PDA

View Full Version : upgrade ammonia plant



mre212
08-07-2019, 12:40 PM
Please help me to know how many KW we can get more by adding economizer to our Ammonia Plant which consist of:

2 MYCOM screw compressors type 200VLD-M @ sst-3 and sdt38
2 MYCOM screw compressors type 200VLD-L @ sst-11 and sdt38

RANGER1
08-07-2019, 09:30 PM
Please help me to know how many KW we can get more by adding economizer to our Ammonia Plant which consist of:

2 MYCOM screw compressors type 200VLD-M @ sst-3 and sdt38
2 MYCOM screw compressors type 200VLD-L @ sst-11 and sdt38

MRE212, As requested

Mycom 200VLD M (recommended L port with & without economiser)
-3 sst without economiser 1063 kw 231 absorbed power
With economiser 1125 kw 235

Mycom 200VLD L (recommended M port with economiser).
-11sst without economiser. 772kw 222kw absorbed
With economiser. 843kw
3550 rpm 936kw absorbed 269kw
economiser 1021kw absorbed 273kw.
Suggest contact Mycom or representative company, as you are asking to much.

mre212
08-07-2019, 11:34 PM
Thank you RANGER for your reply and answer
two compressors from the mentioned above with VSD how much this will adding the capacity?

2 SC NH3 @ -11/+38 for 2 PHE MEG -8/-4°C one to feed Blast cooler, Cold store and the other one to feed Ice bank how much kw +1/+6°C as iced water and if i add another PHE for the ice bank can i get more kw for the same volume

RANGER1
09-07-2019, 07:58 PM
Thank you RANGER for your reply and answer
two compressors from the mentioned above with VSD how much this will adding the capacity?

2 SC NH3 @ -11/+38 for 2 PHE MEG -8/-4°C one to feed Blast cooler, Cold store and the other one to feed Ice bank how much kw +1/+6°C as iced water and if i add another PHE for the ice bank can i get more kw for the same volume

See my previous updated post