14-06-2006, 05:35 AM
G'day,
I've got a problem with hot gas defrost valves blistering the diaphragms that I'm hoping someone may have some thoughts on.
We have machines state wide which are suffering the same problem, and machines Australia wide looked after by other contractors which are suffering a similiar fate.
The unit in question is a frozen beverage dispenser, which uses factory fitted Parker hot gas defrost valves for a ~8 minute defrost every 3 or 4 hours (depending on programming preference). After an average of 8-9 months of operation, the diaphragms blister to the point that they no longer seal off when the solenoid closes - which causes serious capacity problems.
The Parker diaphragms are rated at around 110°C so we tried *ahem* "modifying" Danfoss diaphragms from an EVR6 solenoid (rated 130°C) to fit. The first of these diaphragms failed recently, after just 2 months of operation.
Using temperature sensitive strips, I have proved that the hottest the discharge pipe gets is between 99°C-104°C. During a defrost period, the temperature is below 94°C at both the discharge and the hot gas valve itself (obviously). This suggests that the problem is not neccasarily temperature related.
The unit is on R404A and polyester oil. The distance between compressor discharge and hot gas valve is less than 1000mm and uninsulated.
I've emailed both Parker and Danfoss but havent got a response just yet, although from previous phone conversations I dont think we'll get anything useful.
We are really looking for a better diaphragm material as the company who manufacturers the machine has been fairly unhelpful in this matter and uses any excuse to deny a warranty payment. If we try changing valve bodies or modify the pipework too much, we'll void warranty on the machines we work on. Since some components have a 5 year warranty, we cant go voiding it after the 8 months of operation it takes for the defrost valve to fail. We are trying to help our customers out by replacing the (inadequate?) diaphragms with a better quality item, but unfortunately need to do so without changing to a direct acting valve.
I am not entirely sure why these valves would be blistering, although we are thinking prehaps the design of the valve and the blast they get from the close proximity to the discharge pipe is the problem. Since the valve allows the gas to shoot vertically up into the face of the diaphragm, could hot oil vapour be carried through at a temperature higher than discharge gas temperatures and "blast" the face of the diaphragm? Could the coating of the material be comprimised by a combination of heat and pressure? Is the sealant used not compatible with R404A (although the packaging / sales pitch says it is)?
I've attached a few pictures of the diaphragms. You can see that the blisters line up with the holes in the brass body.
Thanks in advance for any replies,
Regards,
Andrew
I've got a problem with hot gas defrost valves blistering the diaphragms that I'm hoping someone may have some thoughts on.
We have machines state wide which are suffering the same problem, and machines Australia wide looked after by other contractors which are suffering a similiar fate.
The unit in question is a frozen beverage dispenser, which uses factory fitted Parker hot gas defrost valves for a ~8 minute defrost every 3 or 4 hours (depending on programming preference). After an average of 8-9 months of operation, the diaphragms blister to the point that they no longer seal off when the solenoid closes - which causes serious capacity problems.
The Parker diaphragms are rated at around 110°C so we tried *ahem* "modifying" Danfoss diaphragms from an EVR6 solenoid (rated 130°C) to fit. The first of these diaphragms failed recently, after just 2 months of operation.
Using temperature sensitive strips, I have proved that the hottest the discharge pipe gets is between 99°C-104°C. During a defrost period, the temperature is below 94°C at both the discharge and the hot gas valve itself (obviously). This suggests that the problem is not neccasarily temperature related.
The unit is on R404A and polyester oil. The distance between compressor discharge and hot gas valve is less than 1000mm and uninsulated.
I've emailed both Parker and Danfoss but havent got a response just yet, although from previous phone conversations I dont think we'll get anything useful.
We are really looking for a better diaphragm material as the company who manufacturers the machine has been fairly unhelpful in this matter and uses any excuse to deny a warranty payment. If we try changing valve bodies or modify the pipework too much, we'll void warranty on the machines we work on. Since some components have a 5 year warranty, we cant go voiding it after the 8 months of operation it takes for the defrost valve to fail. We are trying to help our customers out by replacing the (inadequate?) diaphragms with a better quality item, but unfortunately need to do so without changing to a direct acting valve.
I am not entirely sure why these valves would be blistering, although we are thinking prehaps the design of the valve and the blast they get from the close proximity to the discharge pipe is the problem. Since the valve allows the gas to shoot vertically up into the face of the diaphragm, could hot oil vapour be carried through at a temperature higher than discharge gas temperatures and "blast" the face of the diaphragm? Could the coating of the material be comprimised by a combination of heat and pressure? Is the sealant used not compatible with R404A (although the packaging / sales pitch says it is)?
I've attached a few pictures of the diaphragms. You can see that the blisters line up with the holes in the brass body.
Thanks in advance for any replies,
Regards,
Andrew