View Full Version : Systemair chiller code
danyyelmorg
23-04-2019, 03:50 PM
Good: I need help with passwords from a chiller SYSTEMAIR model: AQWL 1604 HSE from 2014 thank you.
TrickyRikki
23-04-2019, 06:22 PM
What controller is on the unit?
danyyelmorg
23-04-2019, 06:35 PM
the controller is a carel pco thanks
TrickyRikki
23-04-2019, 07:28 PM
the controller is a carel pco thanks
in my passwords it just says the default password is "1234"
Thats all i have unfortunately, what issue are you having with the unit?
danyyelmorg
24-04-2019, 03:16 PM
I need the maintenance password to set the temperature probe for the superheat of the electronic expansion valve. This code did not give access thanks
TrickyRikki
24-04-2019, 05:34 PM
I need the maintenance password to set the temperature probe for the superheat of the electronic expansion valve. This code did not give access thanks
have you got a photo of the controller?
danyyelmorg
24-04-2019, 06:29 PM
15388
controller photo
This is the only photo I have.
TrickyRikki
24-04-2019, 09:51 PM
15388
controller photo
This is the only photo I have.
have you got the evd interface? its been a while since i needed to use my interface but im sure you can set the superheat ect on that?
TrickyRikki
24-04-2019, 11:07 PM
If you have the evd interface the 2 passwords you require is:
22 = Service level password
66 = Manufacturer password
Hopefully they will get you where you want/need to be
Brian_UK
25-04-2019, 12:15 AM
If you download the instructions for the eev they will give you the above codes.
TrickyRikki
25-04-2019, 09:24 PM
Did you manage to sort the issue with them codes?
Default CAREL passwords will always be "1234" or "0000" - anything else and they've been configured by the OEM/Panel Builder in order to stop engineers interrogating set points without consulting them!
As above poster mentioned, you can use the EVD display (EVDIS00EN0) to adjust set points such as super heat.
;)
oz4rg
18-09-2019, 09:32 AM
The password for the pco are: Service:1234 or 3711
Manufactor: 4939