View Full Version : Chiller Problem Daikin EWAD350E-SL



yanev22
18-04-2019, 11:08 AM
Hi ,

I am having problem with running chiller Daikin model -EWAD350E-SL

The chiller cannot run in auto mode .

In manual model the chiller reach 10 % power and go in error +C1Cmp1 OffSlidePosSen.

The chiller is used Mcquay screw compressor .

The error cannot be reset and pop up again .

TrickyRikki
18-04-2019, 10:26 PM
Hello,

Your fault code "+C1Cmp1 OffSlidePosSen"

Trigger: Sensor shorted or open
Action Taken: Rapid stop compressor
Reset: This alarm can be cleared manually via the keypad, but only if the sensor
is back in range.

Hope that gives you some more information

yanev22
19-04-2019, 04:51 AM
I try to clear this error many times but it show it again

Brian_UK
19-04-2019, 01:56 PM
Have you checked the sensor?

TrickyRikki
19-04-2019, 10:22 PM
I try to clear this error many times but it show it again

It will only stay clear once the sensor is back in range, have you tested it?

expected range is 4 to 20mA.

yanev22
22-04-2019, 12:26 PM
How can be tested ?

Anyone have electric diagram for this model chiller ?