View Full Version : Gree Multi over cooling



Gary
10-04-2019, 07:02 PM
A friend has just installed a Gree Multi to service two rooms. One of the rooms seems to be working normally while the other room over cools and freezes the indoor coil. No error codes. Any idea what might cause this?

martinw58
10-04-2019, 08:00 PM
have you checked the interconnecting wiring is not crossed

Gary
10-04-2019, 08:10 PM
I will definitely check that. Thanks.

Gary
13-04-2019, 09:59 PM
You were right. The wires were crossed. We swapped them back and everything works. Thanks.

martinw58
14-04-2019, 04:23 PM
you shod always run each unit independently on first start up this way you will no the piping and wiring are correct