24-01-2019, 10:26 PM
Has anyone looked at this ?

Seems counter intuitive

Brian_UK
25-01-2019, 09:37 AM
Nothing new I think, there's been lots of 'solar' air conditioning pushed over the years.

Can't remember anybody on here having used it though.

r.bartlett
26-01-2019, 08:03 PM
As they have patents on the idea I don't think this is old tech.

Brian_UK
26-01-2019, 10:46 PM
As they have patents on the idea I don't think this is old tech.
Well, we have threads on the subject going back to 2012 and beyond.

r.bartlett
27-01-2019, 11:09 AM
Well, we have threads on the subject going back to 2012 and beyond.

http://www.refrigeration-engineer.com/forums/showthread.php?45549-Solar-assisted-condenser&highlight=solar

r.bartlett
27-01-2019, 09:21 PM
the old thread has been closed but I think it should be opened up again for discussion. It seems the case studies are proving it to work...?

https://www.solxenergy.com/images/solxenergy/downloads/Case-Studies/AC-Refrigeration/Case-Study-Whitehorse.pdf
https://www.solxenergy.com/images/solxenergy/downloads/Case-Studies/AC-Refrigeration/Evaluation-Toyota-RTE-Report.pdf
https://www.solxenergy.com/images/solxenergy/downloads/Case-Studies/AC-Refrigeration/Case-Study-Sodexo-MOD-3.pdf

I'm curious as the case studies appear quite conclusive and independent. if you have a technical argument other than just poo poo'ing it because it doesn't sound 'right' please feel free to shoot it down technically as I'm interested in it

Segei
29-01-2019, 12:33 AM
Let's have a look at their statements.
1. Compressor heats refrigerant and solar panel will assist him to do that. This is wrong. Compressor compresses refrigerant and refrigerant temperature increase is side effect. It doesn't matter how much you heat refrigerant, it will not liquefied in condenser unless it will be compressed.
2. Delta T will increase. Condenser delta T is temperature difference between condensing temperature and air temperature. 105C is not condensing temperature. This is temperature of super heated refrigerant. Like in any condenser this refrigerant will be cooled down to 50C to initiate condensation process.

How do they created all numbers to show that this approach save energy? I don't know but it can be reduction of refrigeration loads or they just install regular solar panels to produce electricity and offset energy used by refrigeration plant.

Peter_1
01-02-2019, 08:44 AM
If you reheat superheated gasses with an external source after leaving the evaporator, then you're moving horizontally moving to the right along the LP line of the log p/h. This super-superheated gas then enters the compressors. For me resulting in extreme discharge temperatures and lower COP because compressor needs tot pump even more expanded gas which didn't contributed to the cooling process.

r.bartlett
02-02-2019, 08:10 AM
Let's have a look at their statements.
1. Compressor heats refrigerant and solar panel will assist him to do that. This is wrong. Compressor compresses refrigerant and refrigerant temperature increase is side effect. It doesn't matter how much you heat refrigerant, it will not liquefied in condenser unless it will be compressed.
2. Delta T will increase. Condenser delta T is temperature difference between condensing temperature and air temperature. 105C is not condensing temperature. This is temperature of super heated refrigerant. Like in any condenser this refrigerant will be cooled down to 50C to initiate condensation process.

How do they created all numbers to show that this approach save energy? I don't know but it can be reduction of refrigeration loads or they just install regular solar panels to produce electricity and offset energy used by refrigeration plant.

The results are by independent testers. The chance that all these places suddenly had a 'reduced load' or hid PV somewhere simply doesn't make sense.

r.bartlett
02-02-2019, 08:13 AM
If you reheat superheated gasses with an external source after leaving the evaporator, then you're moving horizontally moving to the right along the LP line of the log p/h. This super-superheated gas then enters the compressors. For me resulting in extreme discharge temperatures and lower COP because compressor needs tot pump even more expanded gas which didn't contributed to the cooling process.

the heating takes place in the discharge line.

https://www.solxenergy.com/index.php/how-it-works
http://www.solarcoolmauritius.com/download/How-it-works-1.0.pdf

r.bartlett
02-02-2019, 08:29 AM
https://twitter.com/coolmauritius/status/917442149985275908

Segei
02-02-2019, 09:53 PM
You can test this approach yourself. Put electrical heater in discharge line of the existing system and energy use should drop. Don't count energy used by the heater. However, I'm doubt that this will happen.
Regarding independent testers. I used to believe my eyes (knowledge and experience). If I see it is red, I believe it is red and doesn't matter how many independent tester tell that this is green. I don't see any engineering explanation of this "phenomena".

r.bartlett
04-02-2019, 05:45 PM
No nor me but there seems to be a bank of test cases

https://scontent.fmad3-7.fna.fbcdn.net/v/t1.15752-9/51421989_1989637171341331_90021238918873088_n.jpg?_nc_cat=100&_nc_eui2=AeFh01agEzqJfthUSxVqTd_7DohX3eK2v4XhoNempgCtlZgbXq_lyymm0dAtBCOZL7VOThrWzFKioL3dRQQrxArfRDi-IwadjVscl1K59CaBIQ&_nc_ht=scontent.fmad3-7.fna&oh=b4209daf5043f20d4e43129d83d79397&oe=5CEAD906

"Richard.........Its no joke the technology reallys works and wroks great. Here is a link to the website case study files and attached are just 2 of our own case studies here in The Bahamas and hope this helps."

https://scontent.fmad3-6.fna.fbcdn.net/v/t1.15752-9/51227918_245077426402681_419711866386776064_n.jpg?_nc_cat=109&_nc_eui2=AeGbYn6Bb9uz5QPgLcLF2FchA-OeZzdxehsJ-sRK5YB8_bRdeeS5C3QadxMrquT7Oucldtp4um7brD6_ahETGeyJ8O7_N7DXTcP_Cn28qYKAQw&_nc_ht=scontent.fmad3-6.fna&oh=e32ef4b0f336a77f0abccba03a6a5905&oe=5CE63DBB

r.bartlett
06-02-2019, 03:49 PM
You can test this approach yourself. Put electrical heater in discharge line of the existing system and energy use should drop. Don't count energy used by the heater. However, I'm doubt that this will happen.
.

Apparently this method is possible to try this and see if it works..