OkonedoCharles
31-12-2018, 03:36 AM
Good morning All.
Can someone assist please.
I have this 30gtn carrier chiller, it trips breaker immediately it wanted to start running.
I have checked all Fan Motor and Compressor for Short and they are ok.
Only one compressor is bad and I have disconnected it from the system.
All relays have been checked.
Please can someone assist me on what to do. Thanks

Grizzly
31-12-2018, 09:41 AM
Your Earlier posts say it all Charles.
Good day Engineers
Please I need urgent help.
I'm not that grounded in electrical.

I connected a compressor today and the result was a blast.. Breakers trip and compressor burnt.


what you are now getting I assume?
Is as a direct result of your previous actions.

Knowing when to stop is sometimes as important as knowing what to do.

Enlist the help of local more knowledgeable colleagues.



Grizzly

OkonedoCharles
31-12-2018, 05:03 PM
Grizzly good pm,
Though I'm not grounded in electrical but I understand it because I read and learn everyday.
I only asked questions because I want to know more.
I was expecting someone who has experience same problem to tell me the possible causes.

Brian_UK
31-12-2018, 11:24 PM
You've checked for shorts but have you checked the starters?

Is the supply voltage correct and strong enough?

Switch off/remove fuses to the compressors etc. Start up and recheck the starters for continuity.

Gibbo
01-01-2019, 06:21 PM
Get hold of Mandola's in Lagos as the local Carrier dealer they should be able to solve this problem. You seem out if your depth.

Gibbo.

Gibbo
01-01-2019, 06:22 PM
Mandilas in Lagos.

chemi-cool
01-01-2019, 07:43 PM
Check that your electric supply has 3 phases.
You might have lost one when it tripped the first time.

OkonedoCharles
03-01-2019, 08:09 PM
Thanks a lot Mr Brian _UK

OkonedoCharles
03-01-2019, 08:12 PM
Thanks Mr Gibbo, I'm a staff of Mandilas Enterprises Limited. Carrier Division, Lagos

OkonedoCharles
03-01-2019, 08:13 PM
Chemi cool thanks a lot