View Full Version : Back-up / over-ride settings



CONROD
16-12-2018, 08:19 PM
I have a CO2 rack with a primary and back up control system. The back up contoller acts as a watchdog and takes over from the primary controller if the rack suction pressures increase above set-point for a time period.
As a rule of thumb at what pressure would you expect to see a pack (HT or LT) go into back-up and how long would you expect the time delay to be?

HVACRsaurus
17-12-2018, 07:39 PM
Howdy,

Cut in 3800kPa Cut out 3600kPa (bottom of page 32);
https://www.bitzer.de/shared_media/documentation/bao-104-1-au.pdf