View Full Version : Clivet Chiller



chillermac
10-12-2018, 11:02 AM
HI all,

Got a call to look at a chiller last week. I haven't done any works on these Clivet chillers.
Model # WSAT-XSC150F

Customer told me that the previous maintenance company said a new EEV was needed.

When I looked at the panel the following error codes are displayed
U1/CMP2
E128 Steeper Mot or Error Alarm

U1/CMP2
E103 Evaporator pressure probe

Just wondering if I should change the EEV, the EEV module and the Evap probe?

Thanks in advanve.

Glenn Moore
11-12-2018, 12:07 AM
Change the evap probe first , if that doesn’t rectify it change the controller . You can get a manual controller handset to drive the stepper valve to see if it’s working most of the stepper valve manufacturers make these testers

chillermac
11-12-2018, 08:05 AM
Hey Glenn, solid advise.
That's interesting on the manual controller.. need to look into that a but more..

CONROD
16-12-2018, 08:23 PM
Motor error may indicate a fault with the stepper motor coil. You could check for continuity between the motor poles. Should have 2 separate motor coils. You may have continuity between terminals 1&3, 2&4 for example.

chillermac
17-12-2018, 06:51 PM
Thank you Conrod,

When I get back to site, likely 2019 now, i'll check this out.

chillermac
17-01-2019, 03:31 PM
Hi Guys, still haven’t got back to this chiller. Waiting on parts.
But I have another error on an identical model as above.
E126 SPI faulty alarm.
Manual says E126 is MAX TS TEE peralarm.
It doesn’t reset. Any idea what this is ?