Can any one help me with this chiller, its the first time ive worked on a daikin chiller.

i had the call for the chiller not working at all, when i arrived the controller had 2 alarms which was +C2 OFFMTRPROTECT and +C1 OFFMTRPROTECT

After further investigation i found that one of the 80amp fuses had blown on circuit 1, i removed the fuse and took the compressor offline so circuit 1 is currently running on 2 compressors.

After about 1/2hour of running i get the +C2 OFFMTRPROTECT alarm again and it shuts circuit 2 down, i have looked online and im not able to find what the fault code is or means.

The controller is also asking for a password which we dont have (just taken site over) without calling daikin applied out to investigate is there anyone on here that has experience or knowledge of these chillers?

Gibbo
15-10-2018, 08:33 AM
I would try 1234 for the password
As for the alarm don't know can't see it in the iom possibly compressor or fan trip.
Gibbo

HVACRsaurus
16-10-2018, 06:45 AM
Hi,

This document has done the rounds, I’m thinking it was originally compiled by one of the members here

http://www.frigoristes.fr/getfile.php?att_id=1441&apli=forum_npds&att_name=Mots%20de%20passe%20pour%20diverses%20marques%20de%20GEG.pdf

GHAZ
16-10-2018, 08:59 PM
Try 5321 if it's microtec 3 Siemens controller, I think the motor protection module has shut it down, the compressor motor might be getting hot or some other safety is linked with the protection module

tsialkoutis
20-10-2018, 11:28 AM
6363: Service password

TrickyRikki
02-11-2018, 10:42 PM
Thanks for the advice, sadly i didnt get chance to go back to site to try this out but they have got the issue sorted.

It was a faulty thermistor on circuit 2 compressor, thanks again for everyones help and advice.

Rik

Brian_UK
03-11-2018, 02:17 PM
Thanks for the update.