View Full Version : Hitachi RAK splits



r.bartlett
24-08-2018, 03:58 PM
chaps

full model RAK 18NH5

Around 10 years, twin split , outdoor won't run but not throwing up a code?

Tayters
25-08-2018, 10:31 AM
Temperature probe out of calibration somewhere?

r.bartlett
26-08-2018, 12:25 PM
Temperature probe out of calibration somewhere?

twin so would expect one to run? both indoor fans operate and no flashing lights..

Tayters
27-08-2018, 07:11 PM
Ah, was thinking more the outdoor unit.
The VRF's need the compressor probe on top to be over 40°C I think it is before they run, not sure on the multi set up though.

al
27-08-2018, 09:02 PM
As per Tayters, Might be no harm to check the sensor on compressor, if it's faulty then no run, no fault shows either if i remember.

r.bartlett
29-08-2018, 04:00 PM
ok I'll check.. bit poor show for them not to integrate a sensor fault in the fault circuit..

Imp
07-09-2018, 04:16 PM
Flashing lights on outdoor PCB. 7 times is abnormal thermistor on those models