View Full Version : Thermo King Spectrum SB mutitemp not cooling



meekertim
15-08-2018, 07:03 PM
I've got a spectrum SB multi-temp SR2. Zone 1 is not cooling and I have almost no temp differential when zone 2 is on and in high speed cool when zone 2 goes into null zone 1 starts to cool good with a temp differential of about 4 degrees but as soon as zone 2 kicks back in my temp differential goes away and zone one starts to warm up. I have changed the hot gas solenoid in zone 1 already and this did nothing. with unit running in high speed cool in both zones suction pressure is high at about 75 psi and discharge is a little low at 200 to 220 psi. the unit passes a full pretrip and a unit running pretrip. any help would be greatly appreciated

cadwaladr
15-08-2018, 09:28 PM
Have you tried pumping it down the compressor and if that pulls a good vacuum open up the suction valve and pump down via the reciever tank outlet,suction seems a little high and the delivery seems low to me.

Shibhrac
15-08-2018, 09:30 PM
is there any error code?

Brian_UK
16-08-2018, 12:14 AM
Never mind the pressures, what's the refrigerant?

cadwaladr
16-08-2018, 09:58 AM
​my guess it will be 404a thats standard in thermo king

meekertim
16-08-2018, 02:42 PM
The refrigerant is R404a
It has no error codes and passes both unit running and nonrunning pretrip tests

cadwaladr
16-08-2018, 06:03 PM
Did you carry out the pump down checks?

Shibhrac
16-08-2018, 10:18 PM
you mean the screen displays 00 code which means there is no fault.

meekertim
17-08-2018, 04:30 PM
no codes at all, screen shows 00! I believe this is because the pretrip individually tests evaps one at a time so if zone 2 is in null and it is testing zone one it's going to cool fine the problem doesn't become present unit you run both zones in cool. and yes compressor pump down good and low side pump down shows good also. I've now checked all hot gas solenoids and liquid line solenoids in both zones for operation and opened them up to look inside could it be liquid return check valve? I would think you would start to get an iced up compressor if this was happening. and I have no indication of that happening

Shibhrac
19-08-2018, 07:39 AM
If all components are in good state and all setting parameters are in correct position as you said and also you are sure about the functionality of solenoids valves, expansion valves..ect .
If you are also sure about the refrigeration charge in terms of mass (not pressure readings only) .it’s better you read the pressure from different spots (location at all zones) so that you can have a clear picture about system behavior when zone 2 kicks off .

cadwaladr
20-08-2018, 07:53 PM
Whats the ambient temperature?