View Full Version : scotsman ac176 as - fault during harvest



Toolman
11-08-2018, 07:01 AM
Hey all , Its been a while but I have a Scotsman AC176 as air cooled icemaker .
It makes ice no problem but fails or goes out on HIGH CONDENSER temp during harvest .
( yes Condenser is clean ) I tried switching it to water cooled to trick it but still failed ?
Ordered new probes ....that was worse it actually didnt even run with them , supplier couldnt tell why but took my $250 for two probes . I can return the probes but Im told the fault is with the PCB , another $480 jesus ! So it adding up and yes I can recover all my money once I fix it .

Wondering if anyone has the resistances for the probes tempted to have a fiddle ? instead of buying new PCB .

HVACRsaurus
12-08-2018, 01:41 AM
Hiya,
It is a different model but resistance should be same,

https://www.scotsman-ice.com/service/Technical%20Training/306456pr.pdf

Page 53 says
32,649 ohms @ 32F (0 Celsius)

Happy tinkering

HVACRsaurus
12-08-2018, 01:57 AM
And,

http://www.refmech.com/wp-content/uploads/2016/11/Scotsman-service-manual.pdf

Page 132 shows Full Resistance Chart (albeit Fahrenheit)