Darrylfb
26-06-2018, 09:19 PM
Hi all.
Sorry for the long post.
Got a VRF that system playing up, every couple of days all indoor units stop producing cold air. Carried out a valve reset twice now and it keeps reoccuring. It works in heating fine. The smaller units produce next to nothing in cooilng and the larger units are cold next to the lev. All controllers show 5°c off coil temperature in test mode.
I replaced an lev on an indoor unit a year ago and its the only unit out of 13 that is producing below 10 off coil. Im guessing i may have got it too hot when braizing it in and now its stuck open.
I carried out the valve reset 3 times today before it all came back on with all units producing around 11 off coil.
The total demand of indoor units is slightly higher than the condenser is capable of but were talking like 1kw, but not all units are ever on at once.
There are no issues at the condenser other than the condenser off coil temp is only around 35°c and ambient was 30°c.
Mitsi technical pointed me towards lev3 on the distribution box and said to release it quarter of a turn but it doesnt seem to help it in any way at all.
Any help appreciated :)
Sorry for the long post.
Got a VRF that system playing up, every couple of days all indoor units stop producing cold air. Carried out a valve reset twice now and it keeps reoccuring. It works in heating fine. The smaller units produce next to nothing in cooilng and the larger units are cold next to the lev. All controllers show 5°c off coil temperature in test mode.
I replaced an lev on an indoor unit a year ago and its the only unit out of 13 that is producing below 10 off coil. Im guessing i may have got it too hot when braizing it in and now its stuck open.
I carried out the valve reset 3 times today before it all came back on with all units producing around 11 off coil.
The total demand of indoor units is slightly higher than the condenser is capable of but were talking like 1kw, but not all units are ever on at once.
There are no issues at the condenser other than the condenser off coil temp is only around 35°c and ambient was 30°c.
Mitsi technical pointed me towards lev3 on the distribution box and said to release it quarter of a turn but it doesnt seem to help it in any way at all.
Any help appreciated :)