PDA

View Full Version : Help trane adaptive control



rodriguesac
21-05-2018, 11:03 AM
Hi, anyone now if it possible to calibrate the reading of the temperature probes and the transducer on this control?
Thanks

al
21-05-2018, 05:04 PM
I think you need Trane tracer software to do anything on these chillers, what problems are you having with it?

rodriguesac
22-05-2018, 03:30 PM
Hi Al, thanks for the replay.
In having a alarm low temperature rfgt, and the probe next to exp valve is reading low then the real temperature. The refrigerant is all inside.

al
22-05-2018, 08:50 PM
Could it just be a faulty probe?