View Full Version : Daikin FTX25K2V1B - Cancel auto restart
gozoboy
02-03-2018, 07:16 PM
Hi all,
Anyone know how to cancel auto-restart function on this model? Went through the service manual but could not find anything.
Tayters
02-03-2018, 08:43 PM
Assuming the field settings are the same across the range, the info I've got for older models is field setting 22-5-02 is factory setting, 22-5-01 to disable it. Might not be the way but the only info I've got, be worth a try.
Cheers,
Andy.
gozoboy
02-03-2018, 09:07 PM
Thanks Andy. Can this be done with the infra-red remote or would I need a wired controller?
Brian_UK
02-03-2018, 10:26 PM
Looks like that model does not allow changing of that function.
Is there a reason why you want to disable it?
gozoboy
03-03-2018, 05:39 AM
The unit is installed in a rented room. Its power supply is switched off whenever the door is opened. But if you leave the room and close the door, power is restored and it will start again.
frank
03-03-2018, 09:31 AM
You could do the start/stop on the door opening by adding a krp board instead of dropping mains power.
Every time you drop mains power you disable the crankcase heater function.
gozoboy
04-03-2018, 03:30 AM
Thanks Frank, will get the krp board.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.