View Full Version : Discharge port adjustment in function of climate conditions
Renata
16-01-2018, 12:04 PM
Anyone knows a on line training or a presential one in Brazil about how to calculate de best discharge port ajustment of screw compressor in function of future climate conditions?
Tks, Renata
HVACRsaurus
16-01-2018, 12:05 PM
Which brand Compressor?
HVACRsaurus
16-01-2018, 12:17 PM
For Mycom;
Pages 2-13 through 2-17 and 4-1 through 4-4
http://www.mayekawausa.com/pdf/tech_data/160-320SCV.pdf
Renata
16-01-2018, 12:37 PM
Bitzer, Mycom, frick, sabroe
Renata
16-01-2018, 01:09 PM
For Mycom, the manual says: "Do not operate the compressor with the Vi at any other setting than the L, M or H
port setting", why it can't operate in a intermediate setting?
HVACRsaurus
16-01-2018, 08:33 PM
It can - they are just being conservative / traditional
RANGER1
16-01-2018, 08:47 PM
For Mycom, the manual says: "Do not operate the compressor with the Vi at any other setting than the L, M or H
port setting", why it can't operate in a intermediate setting?
Renata, you can do what you like, but against their recommendation.
As to why, I imagine they have done a lot of testing & they are the best settings to cover everything required.
Why not send them a note to ask why.
"J" series variable auto Vi is like Frick, but of course you would have to use their controller (like Frick). to get optimum result
RANGER1
16-01-2018, 08:56 PM
Bitzer, Mycom, frick, sabroe
Bitzer probably download software on line
Mycom in manual as HVAC indicates, or Mycom selection programme
Frick auto Vi if using their control panel
Sabroe auto Vi uses Unisab, of manual Vi in their maintenance manual
There is a calculation for it which is in most manuals
http://sageenergy.ca/wp-content/uploads/Screw-Gas-Compression-Intro.pdf
http://www.mayekawa.com.au/wordpress/wp-content/uploads/2010/12/V-series-Screw-Compressor.pdf
https://docs.lib.purdue.edu/cgi/viewcontent.cgi?article=1626&context=icec
https://oaktrust.library.tamu.edu/bitstream/handle/1969.1/163383/Vol28015.pdf?sequence=1&isAllowed=y
https://www.irc.wisc.edu/?/paper
07/01/03 3rd from bottom screw efficiencies
Renata
18-01-2018, 10:00 AM
Ranger and HVACR,
I will try these links and recomendation.
thank you very much.
Renata